This is a large storage area adjacent to a locker room. The storage room is divided up into little compartments with chain link 'security mesh' while the locker rooms have certain areas that are solid framed up to 2 ft from the ceiling which is chain link from there on up. I had it originally layed out as if they were not obstructions but now that I'm starting to finalize everything I'm starting to second guess myself and would like to have backup in case plan review questions it.
On Tue, Jul 8, 2014 at 9:19 AM, Steve Leyton <[email protected]> wrote: > I'd take a common sense approach to this. If sprinklers were jammed up > against this type of divider, they could be obstructed. But if storage > height and clearance-to-deflector limits are observed, these don't > present an obstruction. Are you looking at a mini-storage? Over the > years, have done many of these throughout the Southwest and the use of > chain link - either full height or just the top 2 feet of framed > partitions - has been the go-to means of allowing us to stretch out > sprinkler spacing and not end up with mean coverage of 50-75 sq. ft. per > sprinkler. > > Steve Leyton > > > > > > > -----Original Message----- > From: Sprinklerforum > [mailto:[email protected]] On Behalf Of IPA > Sent: Tuesday, July 08, 2014 9:16 AM > To: [email protected] > Subject: Chain Link Partitions in Ord Group II > > Would chain link 'partitions' (full height to ceiling) be considered an > obstruction for a storage area in an ordinary group 2 occupancy? I'm > having a hard time coming up with anything for this and the closest I > can think of is the privacy curtain requirement for light hazard. > > Thanks, > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler > .org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org