Another case of the difference between "when required" and "how to do it".  The 
International Mechanical Code (2012) Sections 510 (Hazardous Exhaust Systems) 
and Section 511 (Dust, Stock and Refuse Conveying Systems) provide guidance on 
this.  Again, it shouldn't be up to a sprinkler contractor to figure out 
whether sprinklers should be installed but only to install per the appropriate 
standard.  As with most of these issues, we don't know if there is a design 
professional on this job or whether your regular customer has just installed a 
new process and has called you to do what's required.  At a minimum you should 
have a copy of the IMC which is enforced for this location.

So, someone (you??) must assess the installation per IMC Section 510/511  from 
end to end.  There is a suppression system reference in Section 510.7.  Some 
determination needs to be made as to whether the materials are "nonflammable 
and noncombustible under all conditions and at any concentration" then make the 
call on suppression.  The entire exhaust system must be engineered to meet the 
performance characteristics in the IMC.

Of course, local code amendments will govern as well as any local AHJ, 
insurance requirements etc.

Sprinkler contractors have a long history of being the can-do guys, with no 
good way to transfer scope responsibility to the right place.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Monday, September 08, 2014 7:43 AM
To: [email protected]
Subject: fume hood / dust collector - sprinklers in?

I have a job where they have a small furnace to create molten metal for 
castings.  There is a hood (2x8ft) above the area where they take the used  
probes  and clean them off.  This duct work goes outside to a dust collector.  
How do I determine if sprinklers are needed in the hood and ductwork?

Thanks,

Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to