Then you only get a break for adjacent hazards or design methods in 11.1.2 for "barriers or partitions capable of delaying heat". But that only helps move the remote area, not necessarily change its final size. Densities would be more affected by this as detailed in the annex example.
Dan W -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Wednesday, October 22, 2014 8:27 AM To: [email protected] Subject: RE: Remote Area & Walls My original question was not about Room Design, I was asking if interior walls came into play when laying out a remote area using the Design Density method. Thanks! Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Wednesday, October 22, 2014 11:22 AM To: [email protected] Subject: RE: Remote Area & Walls I apologize, I missed the "room design" when I read through originally. My statement was for Density/Area. Thanks, Sean Van Gaal Project Manager Nicet III Water-Based System Layout #124801 P: (623) 580-7818 C: (602) 400-4512 F: (623) 434-3154 [email protected] AERO Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix, AZ, 85024 (623) 580-7800 aerofire.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Daniel Wilder Sent: Wednesday, October 22, 2014 8:17 AM To: [email protected] Subject: RE: Remote Area & Walls 13' 13ed 11.2.3.3.3 To utilize the room design method, all rooms shall be enclosed with walls having a fire-resistance rating equal to the water supply duration indicated in Table 11.2.3.1.2. going into 11.2.3.3.5 for non-rated OR self-closing doors...and with unprotected openings (with & without an 8" lintel) for the light hazard side to include an additional 2 heads outside the space OH & EH require automatic or self-closing doors with a rating equal to the water supply duration requirements. Walls and doors/openings come into play Dan W -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Wednesday, October 22, 2014 7:26 AM To: [email protected] Subject: RE: Remote Area & Walls Although I do not think it is expressly stated, I've used the hose durations on the determining factor on if I have to go through fire rated walls. If you have a light hazard occupancy with a 30min hose stream duration requirement, I don't see why you should be expected to calculate heads on the other side that rated wall. However if you have and OH1 hazard, you should calculate through the 1hr rated wall but not a 2+hr rating. Thanks, Sean Van Gaal Project Manager Nicet III Water-Based System Layout #124801 P: (623) 580-7818 C: (602) 400-4512 F: (623) 434-3154 [email protected] AERO Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix, AZ, 85024 (623) 580-7800 aerofire.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Cliff Whitfield Sent: Wednesday, October 22, 2014 6:37 AM To: [email protected] Subject: RE: Remote Area & Walls Brian, >From what I remember, it doesn't matter. Of course, nothing is ever 'black & >white' so there could be several scenarios where the fire walls and their >rating might matter. Unless it was going into an area with a different >occupancy, I would err on the conservative side and be sure I was using the >most demanding area and ignore the walls. Others may have a more 'un-official' stance or different opinion. Cliff Whitfield, SET President Fire Design, Inc. Ph: 719-488-3479 [email protected] www.fire-design.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Wednesday, October 22, 2014 7:31 AM To: [email protected] Subject: RE: Remote Area & Walls Cliff- What about Fire Rated walls? Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Cliff Whitfield Sent: Wednesday, October 22, 2014 9:29 AM To: [email protected] Subject: RE: Remote Area & Walls Brian, Don't have the book in front of me, but this is correct. You would only take the interior walls into account if you were using the 'Room Design Method'. Cliff Whitfield, SET President Fire Design, Inc. Ph: 719-488-3479 [email protected] www.fire-design.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Wednesday, October 22, 2014 7:15 AM To: [email protected] Subject: Remote Area & Walls Apparently sometime in the night the code gremlins snuck in my office and removed pages from my book because I swear I remember reading that when laying out the remote area you do not take into account interior walls but now I can't find it. Anybody? Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org