Dewayne, Looking at this, it depends on the distance the in-rack sprinklers are below the top of storage. For 17.3.4.1.1 the overhead ceiling density could be either .30/2000 or .45/2000. .30/2000 if storage is 5' or less above in-rack sprinklers or .45/2000 if that clearance is over 5' and not more than 10'. See Table 17.3.1.1 for this info.
For 17.3.4.1.4 you are limited to using the .45/2000 requirement regardless of distance of storage to in-rack sprinklers. The distance of storage above in-rack is what will determine which section you use. Thank You, Bob Knight, CET III 208-318-3057 www.Firebyknight.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Wednesday, January 14, 2015 10:05 AM To: SprinklerFORUM Subject: FW: Rack storage question Any takers on this one? *From:* Dewayne Martinez [mailto:[email protected]] *Sent:* Tuesday, January 13, 2015 3:43 PM *To:* '[email protected]' *Subject:* Rack storage question NFPA 13 (07ed) Section 17.3.4.1 I have rack storage of plastic over 25ft high without solid shelves, double row racks,8ft wide aisles. It seems to comply with both 17.3.4.1.1 and 17.3.4.1.4, do I just pick which one works out best for me? Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org