The requirements of 17.3.4.1.1 are considerably more demanding than those outlined in 17.3.4.1.4. I cannot envision a situation where the former would be a more economical solution. The main difference that I can see is that 17.3.4.1.1 applies to "Group A Plastic Commodities" whereas Fig. 17.3.4.1.4 can only be used for "Cartoned Expanded and Unexpanded Plastic and Uncartoned Unexpanded Plastic". This means that if you have Uncartoned Expanded Plastic, you have to use 17.3.4.1.1.
I wish that this section was written more clearly. David -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of James Crawford Sent: Friday, January 16, 2015 7:02 PM To: [email protected] Subject: RE: Rack storage question I have always been under the assumption that it was up to the designer to pick the option that worked the best, as available water pressure, owner requirements and racking design would all play on which option to choose. Some work better than others. Just my opinion Thank you James Crawford Phaser Fire Protection Ltd. Phone 604-888-0318 Fax 604-888-4732 Cel 604-790-0938 Email [email protected] -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Wednesday, January 14, 2015 9:05 AM To: SprinklerFORUM Subject: FW: Rack storage question Any takers on this one? *From:* Dewayne Martinez [mailto:[email protected]] *Sent:* Tuesday, January 13, 2015 3:43 PM *To:* '[email protected]' *Subject:* Rack storage question NFPA 13 (07ed) Section 17.3.4.1 I have rack storage of plastic over 25ft high without solid shelves, double row racks,8ft wide aisles. It seems to comply with both 17.3.4.1.1 and 17.3.4.1.4, do I just pick which one works out best for me? Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org