I believe your Figure numbers are off but the in-rack placement can be per 17.3.4.1.1 OR 17.3.4.1.4
I see the quandary since both say shall be applied. Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Jan 14, 2015, at 9:05 AM, Dewayne Martinez > <[email protected]> wrote: > > Any takers on this one? > > > > *From:* Dewayne Martinez [mailto:[email protected]] > *Sent:* Tuesday, January 13, 2015 3:43 PM > *To:* '[email protected]' > *Subject:* Rack storage question > > > > NFPA 13 (07ed) Section 17.3.4.1 > > I have rack storage of plastic over 25ft high without solid shelves, double > row racks,8ft wide aisles. > > It seems to comply with both 17.3.4.1.1 and 17.3.4.1.4, do I just pick > which one works out best for me? > > Thanks, > > Dewayne > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org