I believe your Figure numbers are off but the in-rack placement can be per 
17.3.4.1.1 OR 17.3.4.1.4

 I see the  quandary since both say shall be applied.



Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Jan 14, 2015, at 9:05 AM, Dewayne Martinez 
> <[email protected]> wrote:
> 
> Any takers on this one?
> 
> 
> 
> *From:* Dewayne Martinez [mailto:[email protected]]
> *Sent:* Tuesday, January 13, 2015 3:43 PM
> *To:* '[email protected]'
> *Subject:* Rack storage question
> 
> 
> 
> NFPA 13 (07ed) Section 17.3.4.1
> 
> I have rack storage of plastic over 25ft high without solid shelves, double
> row racks,8ft wide aisles.
> 
> It seems to comply with both  17.3.4.1.1 and 17.3.4.1.4, do I just pick
> which one works out best for me?
> 
> Thanks,
> 
> Dewayne