I have a job that falls under 16.3.1 (2007 edition), class III rack storage 31' 
high storage with deck height at the peak of 37'. If I look at table 16.3.1.1 
for vertical of 25' & horizontal of 5' it points me to figure 16.3.4.1.1(f). 
Note 7 says that each cube measures 4' to 5', how do I know which it is? If I 
assume each cube is 5' and count up from the floor I would end up at the "B" 
load correct? So I would need (1) row of in rack sprinklers with a (1) face 
sprinkler on each side and (1) longitudinal flue space sprinkler for a total of 
(3) in rack sprinklers at each flue space intersection correct? Any help would 
be greatly appreciated.

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to