I don't have NFPA 13 handy. I think it is like 8.15.xxx or 8.16.xxx. If you 
have the PDF version do a keyword search for "specially listed."  You will see 
that these specific areas require the specially listed sprinklers. Standard 
spray are not acceptable in these shallow, flat areas. 

I've been down this road more times than I can count. I have an informal interp 
from AFSA confirming these are required. I also have a Technical Question 
response answer from NFPA stating the same. 

When using these sprinklers, be careful to note that they must be installed in 
1000 sq ft compartments and require a draft curtain that is 1/3 depth or 8" 
(whichever is greater) to make the compartments of 1000 sq ft. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Jan 16, 2015, at 8:50 AM, Jeremy Frazier <[email protected]> wrote:
> 
> I was always under the impression that you could use a standard spray
> pendent/upright anywhere, and that it was the designers option to use the
> CCS sprinklers or just a standard spray pendent/upright.  (NFPA 2007 8.4.1.1
> "upright and pendent spray sprinklers shall be permited in all occupancy
> hazard classifications and building construction types.)  
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of Travis Mack
> Sent: Wednesday, January 14, 2015 4:25 AM
> To: [email protected]
> Subject: Re: Interstitial Space Between Floors
> 
> If space is <36" clear (54" max) and slope is <2:12 then they are needed. 
> 
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook:
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
> 
> Sent from my iPhone
> 
>> On Jan 13, 2015, at 10:47 AM, Jay White <[email protected]> wrote:
>> 
>> Are you required to use the Specific Application Sprinklers for 
>> Combustible Concealed Spaces between floors? Or can you use a standard 
>> quick response upright?
>> 
>> 
>> 
>> Jay White
>> 
>> Dynamic Fire Protection
>> 
>> 9771 Highway 25 South
>> 
>> Starkville, MS 39759
>> 
>> PH:   662-312-2426
>> 
>> FAX: 662-324-1545
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to