I'm pretty sure you're quoting the appropriate section of the
standard, and it's reference to a listed sprinkler for such spaces is a
bulls eye. The unfortunate extension of this is that the AHJ you're
presenting it to for approval has to be intelligent enough to avoid
making comments such as:
* Tyco is a product manufacture, not an approval laboratory, therefore
their demand area specification is not acceptable.
* The CC2 sprinkler head is not approved by a nationally accepted
approving authority (UL or FM)
* It's Ok to use a "concealed space sprinkler." But it _must_ be
approved (if there is such a thing). Listings and approvals that
only apply to the "service conditions" in Tyco's design manual are
not acceptable. Why is that so hard to understand?
Any plan reviewer who can with two functional eyes look at the catalog
data sheet from Tyco for the CC2, and deny that the sprinkler is
"approved" by an NRTL is going to cause many more problems, and the
concealed space sprinklers are only the beginning.
A good friend encountered these comments in the fall of '14. As I
promised my wife I would stop using that kind of language I found myself
quite unable to compose an appropriate response without referencing acts
that might be anatomically impossible, and are more than likely illegal
in the state in question.
Good luck to Jay, who kicked this thread off!
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/>
***
On 1/19/2015 4:14 AM, Litvak James L. wrote:
>From 2010:
8.15.1.6 Sprinklers used in horizontal combustible concealed
spaces (with a slope not exceeding 2 in 12) with combustible
wood truss or wood joist construction having a combustible
upper surface and where the depth of the space is less
than 36 in. (914 mm) from deck to deck or with double wood
joist construction with a maximum of 36 in. (914 mm) between
the top of the bottom joist and the bottom of the upper
joist shall be listed for such use.
James Litvak
Layout Technician
VSC Fire and Security Co., Inc.
Charlotte Division
(704) 805-9764
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of Travis Mack
Sent: Friday, January 16, 2015 8:15 PM
To: [email protected]
Subject: Re: Interstitial Space Between Floors
I don't have NFPA 13 handy. I think it is like 8.15.xxx or 8.16.xxx. If you have the PDF
version do a keyword search for "specially listed." You will see that these
specific areas require the specially listed sprinklers. Standard spray are not acceptable
in these shallow, flat areas.
I've been down this road more times than I can count. I have an informal interp
from AFSA confirming these are required. I also have a Technical Question
response answer from NFPA stating the same.
When using these sprinklers, be careful to note that they must be installed in 1000
sq ft compartments and require a draft curtain that is 1/3 depth or 8"
(whichever is greater) to make the compartments of 1000 sq ft.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign
Sent from my iPhone
On Jan 16, 2015, at 8:50 AM, Jeremy Frazier <[email protected]> wrote:
I was always under the impression that you could use a standard spray
pendent/upright anywhere, and that it was the designers option to use
the CCS sprinklers or just a standard spray pendent/upright. (NFPA
2007 8.4.1.1 "upright and pendent spray sprinklers shall be permited
in all occupancy hazard classifications and building construction
types.)
-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]]
On Behalf Of Travis Mack
Sent: Wednesday, January 14, 2015 4:25 AM
To: [email protected]
Subject: Re: Interstitial Space Between Floors
If space is <36" clear (54" max) and slope is <2:12 then they are needed.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign
Sent from my iPhone
On Jan 13, 2015, at 10:47 AM, Jay White <[email protected]> wrote:
Are you required to use the Specific Application Sprinklers for
Combustible Concealed Spaces between floors? Or can you use a
standard quick response upright?
Jay White
Dynamic Fire Protection
9771 Highway 25 South
Starkville, MS 39759
PH: 662-312-2426
FAX: 662-324-1545
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
l
er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org