>From 2010: 8.15.1.6 Sprinklers used in horizontal combustible concealed spaces (with a slope not exceeding 2 in 12) with combustible wood truss or wood joist construction having a combustible upper surface and where the depth of the space is less than 36 in. (914 mm) from deck to deck or with double wood joist construction with a maximum of 36 in. (914 mm) between the top of the bottom joist and the bottom of the upper joist shall be listed for such use.
James Litvak Layout Technician VSC Fire and Security Co., Inc. Charlotte Division (704) 805-9764 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack Sent: Friday, January 16, 2015 8:15 PM To: [email protected] Subject: Re: Interstitial Space Between Floors I don't have NFPA 13 handy. I think it is like 8.15.xxx or 8.16.xxx. If you have the PDF version do a keyword search for "specially listed." You will see that these specific areas require the specially listed sprinklers. Standard spray are not acceptable in these shallow, flat areas. I've been down this road more times than I can count. I have an informal interp from AFSA confirming these are required. I also have a Technical Question response answer from NFPA stating the same. When using these sprinklers, be careful to note that they must be installed in 1000 sq ft compartments and require a draft curtain that is 1/3 depth or 8" (whichever is greater) to make the compartments of 1000 sq ft. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone > On Jan 16, 2015, at 8:50 AM, Jeremy Frazier <[email protected]> wrote: > > I was always under the impression that you could use a standard spray > pendent/upright anywhere, and that it was the designers option to use > the CCS sprinklers or just a standard spray pendent/upright. (NFPA > 2007 8.4.1.1 "upright and pendent spray sprinklers shall be permited > in all occupancy hazard classifications and building construction > types.) > > -----Original Message----- > From: Sprinklerforum > [mailto:[email protected]] > On Behalf Of Travis Mack > Sent: Wednesday, January 14, 2015 4:25 AM > To: [email protected] > Subject: Re: Interstitial Space Between Floors > > If space is <36" clear (54" max) and slope is <2:12 then they are needed. > > Travis Mack, SET > MFP Design, LLC > "Follow" us on Facebook: > https://www.facebook.com/pages/MFP-Design-LLC/92218417692 > Send large files to MFP Design via: > https://www.hightail.com/u/MFPDesign > > Sent from my iPhone > >> On Jan 13, 2015, at 10:47 AM, Jay White <[email protected]> wrote: >> >> Are you required to use the Specific Application Sprinklers for >> Combustible Concealed Spaces between floors? Or can you use a >> standard quick response upright? >> >> >> >> Jay White >> >> Dynamic Fire Protection >> >> 9771 Highway 25 South >> >> Starkville, MS 39759 >> >> PH: 662-312-2426 >> >> FAX: 662-324-1545 >> >> >> >> >> >> >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink >> l >> er.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org > > ______________________________________________________________________ > This email has been scanned by the Symantec Email Security.cloud service. > For more information please visit http://www.symanteccloud.com > ______________________________________________________________________ > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
