8.15.1.6 Sprinklers used in horizontal combustible concealed spaces (with a 
slope not exceeding 2 in 12) with combustible wood truss or wood joist 
construction having a combustible upper surface and where the depth of the 
space is lessthan 36 in. (914 mm) from deck to deck or with double woodjoist 
construction with a maximum of 36 in. (914 mm) between the top of the bottom 
joist and the bottom of the upperjoist shall be listed for such use.


R/
Matt

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jeremy Frazier
Sent: Friday, January 16, 2015 8:51 AM
To: [email protected]
Subject: RE: Interstitial Space Between Floors

I was always under the impression that you could use a standard spray 
pendent/upright anywhere, and that it was the designers option to use the CCS 
sprinklers or just a standard spray pendent/upright.  (NFPA 2007 8.4.1.1 
"upright and pendent spray sprinklers shall be permited in all occupancy hazard 
classifications and building construction types.)  

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Travis Mack
Sent: Wednesday, January 14, 2015 4:25 AM
To: [email protected]
Subject: Re: Interstitial Space Between Floors

If space is <36" clear (54" max) and slope is <2:12 then they are needed. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Jan 13, 2015, at 10:47 AM, Jay White <[email protected]> wrote:
> 
> Are you required to use the Specific Application Sprinklers for 
> Combustible Concealed Spaces between floors? Or can you use a standard 
> quick response upright?
> 
> 
> 
> Jay White
> 
> Dynamic Fire Protection
> 
> 9771 Highway 25 South
> 
> Starkville, MS 39759
> 
> PH:   662-312-2426
> 
> FAX: 662-324-1545
> 
> 
> 
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to