Mark - well said. I totally agree. 

Sent from my iPhone

> On Feb 6, 2015, at 6:29 PM, "Mark A. Sornsin, P.E." <masorn...@kfi-eng.com> 
> wrote:
> 
> My two cents is that it is not only the potential stress to the sprinkler 
> from removal/replacement, but the potential for damage during handling.  This 
> is especially true for QR sprinklers.
> 
> From the EOR perspective, I have them replaced with new regardless of if it 
> could be kept in a drop.
> 
> I understand there may be differing perspectives when you are in a 
> competitive bid that doesn't address the issue, or you have an owner griping 
> about every dollar spent.
> 
> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer 
> | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
> http://www.kfiengineers.com
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of accentf...@aol.com
> Sent: Friday, February 06, 2015 4:05 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Relocate sprinklers with drops RETORT
> 
> Good afternoon, All:
> 
> I thought a previous discussion revealed that currently IF the sprinkler 
> stays in the RC, weld-o-let, fitting, etc., then it can be  reinstalled if 
> the sprinkler has not actually been removed from the original  fitting/outlet.
> I believe the concern was the amount of 'stress' applied to the  sprinkler 
> when trying to remove it - and possible damage resulting from the  'torque'.
> Previously, everyone seemed to be on board with this  approach.
> 
> Cordially-
> 
> Jerry
> _accentfire@aol.com_ (mailto:accentf...@aol.com)
> 
> *Jerry D. Watts, SFPE
> President & Co-Founder
> ACCENT FIRE ENGINEERING INT'L. Ltd.**
> Santa Fe, New Mexico USA
> (800) 503.1961 nationwide
> 
> *New Mexico Journeyman Sprinklerfitter Lic.  #08228
> 
> **Licensed Fire Protection Engineers -  Architects/Inspectors/Fire
> Investigators:  AZ  CA  CO   NM  NV  NY  TX  UT  KS  MD  MS
> 
> 
> 
> In a message dated 2/6/2015 2:04:42 P.M. Mountain Standard Time, 
> pe...@waynefire.com writes:
> 
> Based on  the 2nd draft, this is what the 2016 language will say unless it is 
>  Successfully NITMAM ed
> 
> 6.2.1.1*
> When a sprinkler is removed  from a fitting or welded outlet, it shall not be 
> reinstalled except as  permitted by 6.2.1.1.1.
> 6.2.1.1.1
> Dry sprinklers shall be  permitted to be reinstalled when removed in 
> accordance with the manufacturer's  installation and maintenance instructions.
> 
> A.6.2.1.1
> Sprinklers should be permitted to be reinstalled when the sprinkler being 
> removed from the system remains attached to the original fitting or welded 
> outlet, provided care has been taken to ensure the sprinkler has not been 
> damaged. Flexible hose connections are considered a fitting.
> In new  installations, where sprinklers are installed on pendent drop nipples 
> or  sidewall sprinklers prior to final cut-back, protective caps and/or 
> straps  should remain in place until after the drop nipple has been cut to 
> fit to the  final ceiling elevation.
> 
> This is my opinion only and does not  constitute the official opinion of the 
> NFPA.
> 
> Peter Schwab
> VP of  Purchasing & Engineering Technologies
> 
> Wayne Automatic Fire  Sprinklers Inc.
> 222 Capitol Court
> Ocoee, Fl 34761
> 
> Mobile: (407)  468-8248
> Direct: (407) 877-5570
> Fax: (407)  656-8026
> 
> www.waynefire.com
> 
> 
> 
> 
> -----Original  Message-----
> From: Sprinklerforum
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of michael  
> G
> Sent: Friday, February 06, 2015 3:56 PM
> To:  sprinklerforum@lists.firesprinkler.org
> Subject: RE: Relocate sprinklers  with drops
> 
> I would have to agree with Richard,  He is not pulling  the head out of the 
> piping, the Boss of the sprinkler is taking no extra  strain and there is no 
> extra stress added on the sprinkler head its  self.  Only the piping is being 
> removed, cut threaded and  reinstalled.  We basically do this when we install 
> a system....
> 
> We  run the branch line, install a 0-2 and elbow, the drop and a head with 
> the  support ring installed already, so that when we do our initial testing 
> for  leaks, the drops are tested all the way to the sprinkler head. The 
> reason for  this is, 1) to eliminate the number of potential leaks at the end 
> of the job  while conducting the final pressure test. 2) if there is a bad 
> head or  something wrong, i.e.  cracked 1 x 1/2" RC, it is easier to change 
> it out  then, instead of over finished floor and product.
> 
> 
> Mike
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Duane  Johnson
> Sent: Friday, February 06, 2015 3:44 PM
> To:  sprinklerforum@lists.firesprinkler.org
> Subject: RE: Relocate sprinklers  with drops
> 
> 6.2.1.1 (2013) When a sprinkler has been removed for any  reason, it shall 
> not be reinstalled.
> 
> 
> Duane Johnson
> Strickland  Fire Protection
> 
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of  Richard Carr
> Sent: Friday, February 6, 2015 3:38 PM
> To:  sprinklerforum@lists.firesprinkler.org
> Subject: RE: Relocate sprinklers  with drops
> 
> If he is not pulling the head how is it a violation of  NFPA?
> 
> Richard Carr, SET
> Branch Manager
> Cox Fire Protection,  Inc
> 6555 Grace Lane.
> Jacksonville, Fl.  32205
> rc...@coxfire.com
> 904-781-8227
> 
> 
> -----Original  Message-----
> From: Sprinklerforum
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Duane  Johnson
> Sent: Friday, February 06, 2015 3:29 PM
> To:  sprinklerforum@lists.firesprinkler.org
> Subject: RE: Relocate sprinklers  with drops
> 
> The problem is, you won't find this in the standard unless  you print out
> the ROC...
> 
> 
> Duane Johnson
> Strickland Fire  Protection
> 
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Duane  Johnson
> Sent: Friday, February 6, 2015 3:28 PM
> To:  sprinklerforum@lists.firesprinkler.org
> Subject: RE: Relocate sprinklers  with drops
> 
> Not permitted. There was a proposal submitted on the last  cycle to allow
> this, but it was rejected.
> 
> 
> Duane  Johnson
> Strickland Fire Protection
> 
> 
> -----Original  Message-----
> From: Sprinklerforum
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Art  Tiroly
> Sent: Friday, February 6, 2015 3:29 PM
> To:  sprinklerforum@lists.firesprinkler.org
> Subject: RE: Relocate sprinklers  with drops
> 
> I am having an argument with a contractor that is removing  heads and drops
> then moving them to a new position. Sprinklers are QR less  than 5 years
> old.
> He is not removing the head from the drop or the 1x1/2  RC. He says he is
> not reusing sprinklers just relocating them with the drop  nipple. He says
> this is standard practice.
> Does this violate 6.2.1.1? Do  not reuse sprinklers removed from the system.
> 
> 
> Art Tiroly
> ATCO  Fire Protection/Tiroly
> 24400 Highland Rd CLE  44143
> 216-621-8899
> 216-570-7030  cell
> 
> 
> 
> _______________________________________________
> Sprinklerforum  mailing  list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum  mailing  list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum  mailing  list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum  mailing  list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum  mailing  list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum  mailing  list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum  mailing  list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list