Bingo! The influence of the manufactures is overwhelming on the TC however in 
their defense anything that is subjective . . . like how much paint is to much 
paint, needs to be reduced to any amount of paint on a sprinkler requires 
replacement because there are to many variables. I think that same logic 
applies to this topic. 

Can one remove a drop; carefully get it in a 300 machines jaw, make a cut and 
thread, carefully remove it from the machine and re-install the drop. Sure it 
can be done. But it is just as likely that the drop with the head gets 
mishandled and damaged. There are no winners there. I don't read the standard  
as preventing the removal of a drop with the head made in.  But not doing it 
might just be "Best Practice". 

Mike Cabral
Sent from my iPhone

> On Feb 6, 2015, at 6:49 PM, <rfletc...@aerofire.com> <rfletc...@aerofire.com> 
> wrote:
> 
> Like shipping, unpacking and installation only applies the proper and 
> necessary stress for the sprinkler to operate as intended. Or maybe the 
> engineering is so precise that the sprinkler can only stand the rigors of 
> being threaded into a fitting once and then it's useless. Or maybe there are 
> sprinkler manufacturers reps on the 13 committee that know how fragile and 
> un-robust sprinklers are? Why would you build something could only be 
> threaded in once? I'm glad they don't manufacture pipe or fittings.
> 
> Ron fletcher Sent from my iPhone
> 
>> On Feb 6, 2015, at 4:43 PM, John Denhardt <jdenha...@stricklandfire.com> 
>> wrote:
>> 
>> Mark - well said. I totally agree. 
>> 
>> Sent from my iPhone
>> 
>>> On Feb 6, 2015, at 6:29 PM, "Mark A. Sornsin, P.E." <masorn...@kfi-eng.com> 
>>> wrote:
>>> 
>>> My two cents is that it is not only the potential stress to the sprinkler 
>>> from removal/replacement, but the potential for damage during handling.  
>>> This is especially true for QR sprinklers.
>>> 
>>> From the EOR perspective, I have them replaced with new regardless of if it 
>>> could be kept in a drop.
>>> 
>>> I understand there may be differing perspectives when you are in a 
>>> competitive bid that doesn't address the issue, or you have an owner 
>>> griping about every dollar spent.
>>> 
>>> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection 
>>> Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
>>> http://www.kfiengineers.com
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum 
>>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
>>> accentf...@aol.com
>>> Sent: Friday, February 06, 2015 4:05 PM
>>> To: sprinklerforum@lists.firesprinkler.org
>>> Subject: Re: Relocate sprinklers with drops RETORT
>>> 
>>> Good afternoon, All:
>>> 
>>> I thought a previous discussion revealed that currently IF the sprinkler 
>>> stays in the RC, weld-o-let, fitting, etc., then it can be  reinstalled if 
>>> the sprinkler has not actually been removed from the original  
>>> fitting/outlet.
>>> I believe the concern was the amount of 'stress' applied to the  sprinkler 
>>> when trying to remove it - and possible damage resulting from the  'torque'.
>>> Previously, everyone seemed to be on board with this  approach.
>>> 
>>> Cordially-
>>> 
>>> Jerry
>>> _accentfire@aol.com_ (mailto:accentf...@aol.com)
>>> 
>>> *Jerry D. Watts, SFPE
>>> President & Co-Founder
>>> ACCENT FIRE ENGINEERING INT'L. Ltd.**
>>> Santa Fe, New Mexico USA
>>> (800) 503.1961 nationwide
>>> 
>>> *New Mexico Journeyman Sprinklerfitter Lic.  #08228
>>> 
>>> **Licensed Fire Protection Engineers -  Architects/Inspectors/Fire
>>> Investigators:  AZ  CA  CO   NM  NV  NY  TX  UT  KS  MD  MS
>>> 
>>> 
>>> 
>>> In a message dated 2/6/2015 2:04:42 P.M. Mountain Standard Time, 
>>> pe...@waynefire.com writes:
>>> 
>>> Based on  the 2nd draft, this is what the 2016 language will say unless it 
>>> is  Successfully NITMAM ed
>>> 
>>> 6.2.1.1*
>>> When a sprinkler is removed  from a fitting or welded outlet, it shall not 
>>> be reinstalled except as  permitted by 6.2.1.1.1.
>>> 6.2.1.1.1
>>> Dry sprinklers shall be  permitted to be reinstalled when removed in 
>>> accordance with the manufacturer's  installation and maintenance 
>>> instructions.
>>> 
>>> A.6.2.1.1
>>> Sprinklers should be permitted to be reinstalled when the sprinkler being 
>>> removed from the system remains attached to the original fitting or welded 
>>> outlet, provided care has been taken to ensure the sprinkler has not been 
>>> damaged. Flexible hose connections are considered a fitting.
>>> In new  installations, where sprinklers are installed on pendent drop 
>>> nipples or  sidewall sprinklers prior to final cut-back, protective caps 
>>> and/or straps  should remain in place until after the drop nipple has been 
>>> cut to fit to the  final ceiling elevation.
>>> 
>>> This is my opinion only and does not  constitute the official opinion of 
>>> the NFPA.
>>> 
>>> Peter Schwab
>>> VP of  Purchasing & Engineering Technologies
>>> 
>>> Wayne Automatic Fire  Sprinklers Inc.
>>> 222 Capitol Court
>>> Ocoee, Fl 34761
>>> 
>>> Mobile: (407)  468-8248
>>> Direct: (407) 877-5570
>>> Fax: (407)  656-8026
>>> 
>>> www.waynefire.com
>>> 
>>> 
>>> 
>>> 
>>> -----Original  Message-----
>>> From: Sprinklerforum
>>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
>>> michael  G
>>> Sent: Friday, February 06, 2015 3:56 PM
>>> To:  sprinklerforum@lists.firesprinkler.org
>>> Subject: RE: Relocate sprinklers  with drops
>>> 
>>> I would have to agree with Richard,  He is not pulling  the head out of the 
>>> piping, the Boss of the sprinkler is taking no extra  strain and there is 
>>> no extra stress added on the sprinkler head its  self.  Only the piping is 
>>> being removed, cut threaded and  reinstalled.  We basically do this when we 
>>> install a system....
>>> 
>>> We  run the branch line, install a 0-2 and elbow, the drop and a head with 
>>> the  support ring installed already, so that when we do our initial testing 
>>> for  leaks, the drops are tested all the way to the sprinkler head. The 
>>> reason for  this is, 1) to eliminate the number of potential leaks at the 
>>> end of the job  while conducting the final pressure test. 2) if there is a 
>>> bad head or  something wrong, i.e.  cracked 1 x 1/2" RC, it is easier to 
>>> change it out  then, instead of over finished floor and product.
>>> 
>>> 
>>> Mike
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
>>> On Behalf Of Duane  Johnson
>>> Sent: Friday, February 06, 2015 3:44 PM
>>> To:  sprinklerforum@lists.firesprinkler.org
>>> Subject: RE: Relocate sprinklers  with drops
>>> 
>>> 6.2.1.1 (2013) When a sprinkler has been removed for any  reason, it shall 
>>> not be reinstalled.
>>> 
>>> 
>>> Duane Johnson
>>> Strickland  Fire Protection
>>> 
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
>>> On Behalf Of  Richard Carr
>>> Sent: Friday, February 6, 2015 3:38 PM
>>> To:  sprinklerforum@lists.firesprinkler.org
>>> Subject: RE: Relocate sprinklers  with drops
>>> 
>>> If he is not pulling the head how is it a violation of  NFPA?
>>> 
>>> Richard Carr, SET
>>> Branch Manager
>>> Cox Fire Protection,  Inc
>>> 6555 Grace Lane.
>>> Jacksonville, Fl.  32205
>>> rc...@coxfire.com
>>> 904-781-8227
>>> 
>>> 
>>> -----Original  Message-----
>>> From: Sprinklerforum
>>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
>>> On Behalf Of Duane  Johnson
>>> Sent: Friday, February 06, 2015 3:29 PM
>>> To:  sprinklerforum@lists.firesprinkler.org
>>> Subject: RE: Relocate sprinklers  with drops
>>> 
>>> The problem is, you won't find this in the standard unless  you print out
>>> the ROC...
>>> 
>>> 
>>> Duane Johnson
>>> Strickland Fire  Protection
>>> 
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
>>> On Behalf Of Duane  Johnson
>>> Sent: Friday, February 6, 2015 3:28 PM
>>> To:  sprinklerforum@lists.firesprinkler.org
>>> Subject: RE: Relocate sprinklers  with drops
>>> 
>>> Not permitted. There was a proposal submitted on the last  cycle to allow
>>> this, but it was rejected.
>>> 
>>> 
>>> Duane  Johnson
>>> Strickland Fire Protection
>>> 
>>> 
>>> -----Original  Message-----
>>> From: Sprinklerforum
>>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
>>> On Behalf Of Art  Tiroly
>>> Sent: Friday, February 6, 2015 3:29 PM
>>> To:  sprinklerforum@lists.firesprinkler.org
>>> Subject: RE: Relocate sprinklers  with drops
>>> 
>>> I am having an argument with a contractor that is removing  heads and drops
>>> then moving them to a new position. Sprinklers are QR less  than 5 years
>>> old.
>>> He is not removing the head from the drop or the 1x1/2  RC. He says he is
>>> not reusing sprinklers just relocating them with the drop  nipple. He says
>>> this is standard practice.
>>> Does this violate 6.2.1.1? Do  not reuse sprinklers removed from the system.
>>> 
>>> 
>>> Art Tiroly
>>> ATCO  Fire Protection/Tiroly
>>> 24400 Highland Rd CLE  44143
>>> 216-621-8899
>>> 216-570-7030  cell
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> Sprinklerforum  mailing  list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum  mailing  list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum  mailing  list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum  mailing  list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum  mailing  list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> _______________________________________________
>>> Sprinklerforum  mailing  list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> _______________________________________________
>>> Sprinklerforum  mailing  list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> ______________________________________________________________________
>>> This email has been scanned by the Symantec Email Security.cloud service.
>>> For more information please visit http://www.symanteccloud.com
>>> ______________________________________________________________________
>>> 
>>> ______________________________________________________________________
>>> This email has been scanned by the Symantec Email Security.cloud service.
>>> For more information please visit http://www.symanteccloud.com
>>> ______________________________________________________________________
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org