Since NFPA 13 specifically addresses them, as long as the i's are dotted and
t's crossed, why not?

I see a dilemma if the hazard below the ceiling happens to be 'light'.
Section 8.15.15.2  (2013) doesn't allow QR sprinklers to be used above
drop-out ceilings.  So if the hazard happens to be 'light', you could argue
that NFPA 13 provides no acceptable way to protect it.  

Ed Kramer

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Travis Mack
Sent: Monday, April 06, 2015 9:59 AM
To: <[email protected]>
Subject: Melt away ceiling tiles

Is anyone running into these things lately? How are you handling them? 

I have never really been a fan of these things. A customer has a job where
the builder is wanting to use these tiles to eliminate the need for
sprinklers at the ceiling. We did the shell space and there are 155 degree
uprights at the deck. This is 1st floor of a 4 story building. 

The tiles are rated at 165f. The sprinklers will have to be changed to 200F
so the sprinklers will activate after the tiles fall. 

What is your thoughts on these things?

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to