I would not jump to the conclusion that you have to change to a higher temp 
rating.  Must confess, I’ve seen only one drop-out ceiling (well 80% drop-out 
since 8 or 10 standard ceiling tiles had been installed long after the initial 
installation) and this issue has never come up in the last 20 years.

Even at a slightly higher temp rating, the ceiling is still exposed first and 
not sure how much heat gets past it before it drops out.  Any idea what's the 
ceiling RTI rating - lol.

What does the manufacturer data sheet say?  A quick search shows the UL 
certification is based on SR sprinklers with a 165 F rating.

A bigger first question is what is the occupancy classification so as to ensure 
that SR sprinklers are acceptable.  Can not use QR or EC above these ceilings 
(13:8.15.15.2).

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Apr 6, 2015, at 7:59 AM, Travis Mack <[email protected]> wrote:
> 
> Is anyone running into these things lately? How are you handling them? 
> 
> I have never really been a fan of these things. A customer has a job where 
> the builder is wanting to use these tiles to eliminate the need for 
> sprinklers at the ceiling. We did the shell space and there are 155 degree 
> uprights at the deck. This is 1st floor of a 4 story building. 
> 
> The tiles are rated at 165f. The sprinklers will have to be changed to 200F 
> so the sprinklers will activate after the tiles fall. 
> 
> What is your thoughts on these things?
> 
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook: 
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
> 
> Sent from my iPhone
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to