You should have started with this question (since it is the issue).  The Table 
says Combustible Construction so as already identified by Ken you go to the 
definitions.  The only issue that comes to mind where it is the combustibility 
of the framing that drives the criteria is the other (nasty, ultra-ultra 
conservative) attic criteria in 8.6.4.1.4.

Roland
  
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On May 6, 2015, at 10:16 AM, Travis Mack <[email protected]> wrote:
> 
> That was my question. Does the non combustible framing members modify that, 
> or allow for any changes? I am aware of using that for combustible members. 
> 
> Travis Mack, SET