That makes sense. I was grabbing for straws. Customer missed it because of 
steel framing. Didn't catch plywood sheathing. I was hoping to be able to help 
cut down sprinkler count. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On May 6, 2015, at 10:25 AM, Eric V. Tysinger <[email protected]> wrote:
> 
> I would think that the spacing of the members is addressed as potential 
> obstructions. Less than 3' means there are more members between each 
> sprinkler, so the maximum spacing is reduced to lessen the number of 
> obstructions. I don't think the combustibility of the members plays a part. 
> The table only cares if it is non-combustible or combustible construction, 
> obstructed or unobstructed, and the spacing of the members.
> 
> 
> 
> Eric V. Tysinger
> Designer
> Wiginton Fire Systems - Miami, FL
> Email: [email protected]
> Main: 305-888-2402p3416
> Direct: 305-830-0490
> Fax: 305-888-3804
> Mobile: 239-633-9703
> 
> 
> 
> Confidentiality Notice:
> This e-mail message, including any attachments, is for the sole use of the 
> intended recipients and may contain confidential and privileged information. 
> Any unauthorized review, use, disclosure or distribution is prohibited. If 
> you are not the intended recipient, please contact the sender by reply e-mail 
> and destroy all copies of the original message.
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Travis Mack
> Sent: Wednesday, May 06, 2015 1:17 PM
> To: [email protected]
> Subject: Re: Attic
> 
> That was my question. Does the non combustible framing members modify that, 
> or allow for any changes? I am aware of using that for combustible members.
> 
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook: 
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
> 
> Sent from my iPhone
> 
>> On May 6, 2015, at 10:06 AM, Eric V. Tysinger <[email protected]> wrote:
>> 
>> Wouldn't table 8.6.2.2.1(a) indicate 130sqft max?
>> 
>> Combustible, Unobstructed, with exposed members less than 3'-0 on center.
>> 
>> 
>> 
>> 
>> Eric V. Tysinger
>> Designer
>> Wiginton Fire Systems - Miami, FL
>> Email: [email protected]
>> Main: 305-888-2402p3416
>> Direct: 305-830-0490
>> Fax: 305-888-3804
>> Mobile: 239-633-9703
>> 
>> 
>> 
>> Confidentiality Notice:
>> This e-mail message, including any attachments, is for the sole use of the 
>> intended recipients and may contain confidential and privileged information. 
>> Any unauthorized review, use, disclosure or distribution is prohibited. If 
>> you are not the intended recipient, please contact the sender by reply 
>> e-mail and destroy all copies of the original message.
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:[email protected]] On Behalf Of
>> Travis Mack
>> Sent: Wednesday, May 06, 2015 12:43 PM
>> To: [email protected]
>> Subject: Re: Attic
>> 
>> It is not fire treated. I already tried that route. I feel like 225 would be 
>> acceptable. Which also begs the question, would ex cov be acceptable? It is 
>> unobstructed construction. I believe the ex cov sprinklers are allowed for 
>> unobstructed combustible.
>> 
>> Just a rare situation.
>> 
>> Travis Mack, SET
>> MFP Design, LLC
>> "Follow" us on Facebook:
>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>> Send large files to MFP Design via:
>> https://www.hightail.com/u/MFPDesign
>> 
>> Sent from my iPhone
>> 
>>> On May 6, 2015, at 9:21 AM, Todd - Work <[email protected]> wrote:
>>> 
>>> Good question. I think you could go to 225, but the Book doesn't
>>> address it. I assume the plywood is not fire treated? Most of the
>>> times I see this arrangement, the plywood is treated.
>>> 
>>> Todd G Williams, PE
>>> Fire Protection Design/Consulting
>>> Stonington, CT
>>> www.fpdc.com
>>> 860-535-2080 (ofc)
>>> 860-608-4559 (cell)
>>> Sent using CloudMagic
>>> [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
>>> On Wed, May 6, 2015 at 12:04 PM,
>>> [email protected]
>>> <[email protected]> wrote:
>>> For an attic with light gauge steel trusses spaced 24" on center and
>>> plywood deck sheathing, would the spacing be limited to 130 sq ft or
>>> would 225 be acceptable? Slope is 3:12.
>>> 
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> "Follow" us on Facebook:
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>> Send large files to MFP Design via:
>>> https://www.hightail.com/u/MFPDesign
>>> 
>>> Sent from my iPhone
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> l er.org _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> l
>>> er.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to