That would be my thoughts as well, but there doesn't appear to be wording in the standard that indicates such. Therefore, I will have to defer to the letter of the standard and stick with 130 max spacing.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 5/6/2015 11:19 AM, Brad Casterline wrote:
Unobstructed means just that.
Noncomb. members means no closley spaced, light, fast burning 'kindling'.
I would vote 225 sf max if my vote counted.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Travis Mack
Sent: Wednesday, May 06, 2015 12:40 PM
To: [email protected]
Subject: Re: Attic

That makes sense. I was grabbing for straws. Customer missed it because of
steel framing. Didn't catch plywood sheathing. I was hoping to be able to
help cut down sprinkler count.

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On May 6, 2015, at 10:25 AM, Eric V. Tysinger <[email protected]> wrote:

I would think that the spacing of the members is addressed as potential
obstructions. Less than 3' means there are more members between each
sprinkler, so the maximum spacing is reduced to lessen the number of
obstructions. I don't think the combustibility of the members plays a part.
The table only cares if it is non-combustible or combustible construction,
obstructed or unobstructed, and the spacing of the members.


Eric V. Tysinger
Designer
Wiginton Fire Systems - Miami, FL
Email: [email protected]
Main: 305-888-2402p3416
Direct: 305-830-0490
Fax: 305-888-3804
Mobile: 239-633-9703



Confidentiality Notice:
This e-mail message, including any attachments, is for the sole use of the
intended recipients and may contain confidential and privileged information.
Any unauthorized review, use, disclosure or distribution is prohibited. If
you are not the intended recipient, please contact the sender by reply
e-mail and destroy all copies of the original message.
-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Travis
Mack
Sent: Wednesday, May 06, 2015 1:17 PM
To: [email protected]
Subject: Re: Attic

That was my question. Does the non combustible framing members modify
that, or allow for any changes? I am aware of using that for combustible
members.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On May 6, 2015, at 10:06 AM, Eric V. Tysinger <[email protected]> wrote:

Wouldn't table 8.6.2.2.1(a) indicate 130sqft max?

Combustible, Unobstructed, with exposed members less than 3'-0 on center.




Eric V. Tysinger
Designer
Wiginton Fire Systems - Miami, FL
Email: [email protected]
Main: 305-888-2402p3416
Direct: 305-830-0490
Fax: 305-888-3804
Mobile: 239-633-9703



Confidentiality Notice:
This e-mail message, including any attachments, is for the sole use of
the intended recipients and may contain confidential and privileged
information. Any unauthorized review, use, disclosure or distribution is
prohibited. If you are not the intended recipient, please contact the sender
by reply e-mail and destroy all copies of the original message.
-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Travis Mack
Sent: Wednesday, May 06, 2015 12:43 PM
To: [email protected]
Subject: Re: Attic

It is not fire treated. I already tried that route. I feel like 225 would
be acceptable. Which also begs the question, would ex cov be acceptable? It
is unobstructed construction. I believe the ex cov sprinklers are allowed
for unobstructed combustible.
Just a rare situation.

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On May 6, 2015, at 9:21 AM, Todd - Work <[email protected]> wrote:

Good question. I think you could go to 225, but the Book doesn't
address it. I assume the plywood is not fire treated? Most of the
times I see this arrangement, the plywood is treated.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
On Wed, May 6, 2015 at 12:04 PM,
[email protected]
<[email protected]> wrote:
For an attic with light gauge steel trusses spaced 24" on center and
plywood deck sheathing, would the spacing be limited to 130 sq ft or
would 225 be acceptable? Slope is 3:12.

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
l er.org _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
l
er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to