Just to be clear this is a Listed product, not a whole lot of debate here. 
Nowhere does it say UL Listing. The only requirement really where the AHJ comes 
in is "included in a list published by an organization that is acceptable to 
the authority having jurisdiction".  The only debate might be if LPCB is 
acceptable to the AHJ.  I believe an AHJ (US Fire Marshal or the like) would 
lose every time if they tried to not accept.  You need approval of LPCB, not 
the application of this product.

That said I agree with those questioning the need for anything but a plain wet 
head.  Whenever faced with this I ask the owner how they were dealing with a 
power outage or roof leak as examples. With some thinking they always back off 
and put their money toward protecting their valuable information from ALL 
causes of loss not just an irrational fear of sprinklers. 

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Pat Thompson
Sent: Monday, June 15, 2015 11:40 AM
To: [email protected]
Subject: RE: 

We have used this set up for up to 3 sprinklers in 'computer rooms'. Approval 
was given by local AHJ of the idea after some discussion as it is not a listed 
application. 

A good idea is to install a small drain (1/2 inch) on the drop nipple to the 
sprinklers to allow draining after testing or activation; after all the idea is 
to keep water out of their precious room. Also, a gauge downstream of the 
solenoid to allow visual indication of the pipe being charged. Both these 
features are located above the drop tile ceiling. 

The AHJ asked for a UL listed 24VDC solenoid that is normally open - power 
holds it closed. By doing so it is 'fail safe', that is to say that in the case 
of panel failure or power loss the water will reach the sprinklers. A small 
conventional control panel with smoke or heat detection for automatic 
activation is all that is needed, the solenoid circuit is on a relay that opens 
upon fire detection.

One drawback is that 24 hours of standby is required in the battery set in 
order to hold the solenoid. Because of the current draw of the solenoid this 
results in the batteries being larger than what will fit into the panel 
enclosure, requiring a separate battery cabinet to house the batteries.

Cheers,

Pat Thompson
ATS Alaska
Direct: 907-375-4176

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of teemsprinkdave
Sent: Monday, June 15, 2015 7:09 AM
To: FORUM
Subject: 

Needing a little help, I have a customer wanting to make a small room into a 
computer server room. One sprinkler in the room. Has anybody used a solenoid 
valve, normally closed, and activated by a heat detector? Trying to save the 
expense of a pre-action system.
  DAVE GROVER
Teem Sprinkler Co.
Superintendent 
NFPA 25 Level II Inspector
P 336-650-9005
F 336-650-9007
C 336-399-9006
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to