And I'll question the ability of most AHJs to make the call regarding
suitability. Maybe I'll trust Chris, or the Chris that's the FPE for the
City of Tacoma, but I know better about the guys in many local
jurisdictions. People who the Wizard has given gold badges to. Bet this
wouldn't have been allowed if the FM/AHJ was held liable if something went
wrong. Like the Second Amendment there are two clauses in play. If I may
add a qualifier or two:

"...either..."

1. "...the equipment, material, or service meets appropriate designated
standards..."

"...or..."

2. "...has been tested and found suitable for a specified purpose."

1. Does it meet the standards? What QUALIFIED person said if it
isn't listed by a nationally recognized lab?

or

2. Has it been TESTED and and found suitable? And by whom?

On Tue, Jun 16, 2015 at 8:24 AM, Damien Shannon <[email protected]>
wrote:

> I agree Chris that the wording you referenced is as strong a language on
> the matter the seems to be in NFPA 13.
>
> It does however seem to lead to a 'grey' zone. While the suitability of the
> device is question maybe black and white, the fact that NFPA 13 thereby
> (Section 6.1) allows components that may be listed for a different
> standard, seems to require someone (individual rather than lab), i.e.
> either the contractor or the AHJ to be making the determination as to
> whether it '...found suitable for a specified purpose.
>
> Learned something new today. I didn't think the system being described
> would have met the requirements for an NFPA 13 installation without
> requiring treating it as an 'equivalency' (section 1.5).
>
> Thank you.
>
> Best Regards.
>
> Damien Shannon.
>
>
>
> On 16 June 2015 at 15:57, Cahill, Christopher <[email protected]>
> wrote:
>
> > "states that either the equipment, material, or service meets appropriate
> > designated standards or has been tested and found suitable for a
> specified
> > purpose."
> >
> > I take that to mean it's questionable to use a 5 psi head in an NFPA 13
> > system.  However, the device suggested I think meets the part about
> "found
> > suitable for a specified purpose".
> >
> > Chris Cahill, PE*
> > Associate Fire Protection Engineer
> > Burns & McDonnell
> > Phone:  952.656.3652
> > Fax:  952.229.2923
> > [email protected]
> > www.burnsmcd.com
> > *Registered in: MN
> >
> >
> > Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For
> >
> >
> > -----Original Message-----
> > From: Sprinklerforum [mailto:
> > [email protected]] On Behalf Of Damien
> > Shannon
> > Sent: Tuesday, June 16, 2015 9:27 AM
> > To: [email protected]
> > Subject: Re:
> >
> > I would have thought that if the contractor is to provide an NFPA 13
> > compliant system, then I would think the listing of a product would have
> to
> > specifically state that it is listed for use in an NFPA 13 system (maybe
> it
> > does, I haven't seen the datasheet on the valve in question); without
> > getting into dealing with it as an 'Equivalency'.
> >
> > Most of the LPCB Approvals I have seen are for installation in accordance
> > with EN12845, but maybe the product being discussed has LPCB Approval for
> > NFPA 13 also.
> >
> > There are so many aspects that NFPA 13 & EN12845 (which is is the
> > Installation Standard that LPCB usually seem to 'Approve' components for
> > use), are so very different that it would seem strange to think you can
> > just start using LPCB Approved parts in an NFPA 13 system. Example
> > 'Conventional Sprinklers' (aka 'Old Style' sprinklers) are approved and
> > common place in EN12845 in a lot of occupancies. The also only require 5
> > psi minimum sprinkler pressure rather than 7psi. They allow sprinklers at
> > different distances from the ceiling...
> >
> > In the past I have not used parts that have not specifically mentioned on
> > the product datasheet that the listing in for use in an NFPA 13 system
> (or
> > EN12845/FM 2-0 when working on those projects). Have I been incorrect in
> > this regards?
> >
> > Regards.
> >
> > Damien Shannon.
> >
> > On 16 June 2015 at 13:46, Cahill, Christopher <[email protected]>
> > wrote:
> >
> > > Just to be clear this is a Listed product, not a whole lot of debate
> > here.
> > > Nowhere does it say UL Listing. The only requirement really where the
> > > AHJ comes in is "included in a list published by an organization that
> > > is acceptable to the authority having jurisdiction".  The only debate
> > > might be if LPCB is acceptable to the AHJ.  I believe an AHJ (US Fire
> > > Marshal or the
> > > like) would lose every time if they tried to not accept.  You need
> > > approval of LPCB, not the application of this product.
> > >
> > > That said I agree with those questioning the need for anything but a
> > > plain wet head.  Whenever faced with this I ask the owner how they
> > > were dealing with a power outage or roof leak as examples. With some
> > > thinking they always back off and put their money toward protecting
> > > their valuable information from ALL causes of loss not just an
> > > irrational fear of sprinklers.
> > >
> > > Chris Cahill, PE*
> > > Associate Fire Protection Engineer
> > > Burns & McDonnell
> > > Phone:  952.656.3652
> > > Fax:  952.229.2923
> > > [email protected]
> > > www.burnsmcd.com
> > > *Registered in: MN
> > >
> > >
> > > Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work
> > > For
> > >
> > >
> > > -----Original Message-----
> > > From: Sprinklerforum [mailto:
> > > [email protected]] On Behalf Of Pat
> > > Thompson
> > > Sent: Monday, June 15, 2015 11:40 AM
> > > To: [email protected]
> > > Subject: RE:
> > >
> > > We have used this set up for up to 3 sprinklers in 'computer rooms'.
> > > Approval was given by local AHJ of the idea after some discussion as
> > > it is not a listed application.
> > >
> > > A good idea is to install a small drain (1/2 inch) on the drop nipple
> > > to the sprinklers to allow draining after testing or activation; after
> > > all the idea is to keep water out of their precious room. Also, a
> > > gauge downstream of the solenoid to allow visual indication of the
> > > pipe being charged. Both these features are located above the drop tile
> > ceiling.
> > >
> > > The AHJ asked for a UL listed 24VDC solenoid that is normally open -
> > > power holds it closed. By doing so it is 'fail safe', that is to say
> > > that in the case of panel failure or power loss the water will reach
> > > the sprinklers. A small conventional control panel with smoke or heat
> > > detection for automatic activation is all that is needed, the solenoid
> > > circuit is on a relay that opens upon fire detection.
> > >
> > > One drawback is that 24 hours of standby is required in the battery
> > > set in order to hold the solenoid. Because of the current draw of the
> > > solenoid this results in the batteries being larger than what will fit
> > > into the panel enclosure, requiring a separate battery cabinet to
> > > house the batteries.
> > >
> > > Cheers,
> > >
> > > Pat Thompson
> > > ATS Alaska
> > > Direct: 907-375-4176
> > >
> > > -----Original Message-----
> > > From: Sprinklerforum [mailto:
> > > [email protected]] On Behalf Of
> > > teemsprinkdave
> > > Sent: Monday, June 15, 2015 7:09 AM
> > > To: FORUM
> > > Subject:
> > >
> > > Needing a little help, I have a customer wanting to make a small room
> > > into a computer server room. One sprinkler in the room. Has anybody
> > > used a solenoid valve, normally closed, and activated by a heat
> > > detector? Trying to save the expense of a pre-action system.
> > >   DAVE GROVER
> > > Teem Sprinkler Co.
> > > Superintendent
> > > NFPA 25 Level II Inspector
> > > P 336-650-9005
> > > F 336-650-9007
> > > C 336-399-9006
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > > er.org _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > > er.org _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > > er.org
> > >
> >
> >
> >
> > --
> >
> > *Damien Shannon*
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
>
>
>
> --
>
> *Damien Shannon*
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • RE: Pat Thompson
    • RE: Cahill, Christopher
      • Re: Roland Huggins
        • Re: rongreenman .
          • Re: Roland Huggins
      • Re: Damien Shannon
        • RE: Re: Cahill, Christopher
          • Re: Re: Damien Shannon
            • Re: Re: rongreenman .
  • Re: Roland Huggins

Reply via email to