"states that either the equipment, material, or service meets appropriate 
designated standards or has been tested and found suitable for a specified 
purpose."

I take that to mean it's questionable to use a 5 psi head in an NFPA 13 system. 
 However, the device suggested I think meets the part about "found suitable for 
a specified purpose".

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652    
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Damien Shannon
Sent: Tuesday, June 16, 2015 9:27 AM
To: [email protected]
Subject: Re:

I would have thought that if the contractor is to provide an NFPA 13 compliant 
system, then I would think the listing of a product would have to specifically 
state that it is listed for use in an NFPA 13 system (maybe it does, I haven't 
seen the datasheet on the valve in question); without getting into dealing with 
it as an 'Equivalency'.

Most of the LPCB Approvals I have seen are for installation in accordance with 
EN12845, but maybe the product being discussed has LPCB Approval for NFPA 13 
also.

There are so many aspects that NFPA 13 & EN12845 (which is is the Installation 
Standard that LPCB usually seem to 'Approve' components for use), are so very 
different that it would seem strange to think you can just start using LPCB 
Approved parts in an NFPA 13 system. Example 'Conventional Sprinklers' (aka 
'Old Style' sprinklers) are approved and common place in EN12845 in a lot of 
occupancies. The also only require 5 psi minimum sprinkler pressure rather than 
7psi. They allow sprinklers at different distances from the ceiling...

In the past I have not used parts that have not specifically mentioned on the 
product datasheet that the listing in for use in an NFPA 13 system (or 
EN12845/FM 2-0 when working on those projects). Have I been incorrect in this 
regards?

Regards.

Damien Shannon.

On 16 June 2015 at 13:46, Cahill, Christopher <[email protected]> wrote:

> Just to be clear this is a Listed product, not a whole lot of debate here.
> Nowhere does it say UL Listing. The only requirement really where the 
> AHJ comes in is "included in a list published by an organization that 
> is acceptable to the authority having jurisdiction".  The only debate 
> might be if LPCB is acceptable to the AHJ.  I believe an AHJ (US Fire 
> Marshal or the
> like) would lose every time if they tried to not accept.  You need 
> approval of LPCB, not the application of this product.
>
> That said I agree with those questioning the need for anything but a 
> plain wet head.  Whenever faced with this I ask the owner how they 
> were dealing with a power outage or roof leak as examples. With some 
> thinking they always back off and put their money toward protecting 
> their valuable information from ALL causes of loss not just an 
> irrational fear of sprinklers.
>
> Chris Cahill, PE*
> Associate Fire Protection Engineer
> Burns & McDonnell
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
> *Registered in: MN
>
>
> Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work 
> For
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Pat 
> Thompson
> Sent: Monday, June 15, 2015 11:40 AM
> To: [email protected]
> Subject: RE:
>
> We have used this set up for up to 3 sprinklers in 'computer rooms'.
> Approval was given by local AHJ of the idea after some discussion as 
> it is not a listed application.
>
> A good idea is to install a small drain (1/2 inch) on the drop nipple 
> to the sprinklers to allow draining after testing or activation; after 
> all the idea is to keep water out of their precious room. Also, a 
> gauge downstream of the solenoid to allow visual indication of the 
> pipe being charged. Both these features are located above the drop tile 
> ceiling.
>
> The AHJ asked for a UL listed 24VDC solenoid that is normally open - 
> power holds it closed. By doing so it is 'fail safe', that is to say 
> that in the case of panel failure or power loss the water will reach 
> the sprinklers. A small conventional control panel with smoke or heat 
> detection for automatic activation is all that is needed, the solenoid 
> circuit is on a relay that opens upon fire detection.
>
> One drawback is that 24 hours of standby is required in the battery 
> set in order to hold the solenoid. Because of the current draw of the 
> solenoid this results in the batteries being larger than what will fit 
> into the panel enclosure, requiring a separate battery cabinet to 
> house the batteries.
>
> Cheers,
>
> Pat Thompson
> ATS Alaska
> Direct: 907-375-4176
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of 
> teemsprinkdave
> Sent: Monday, June 15, 2015 7:09 AM
> To: FORUM
> Subject:
>
> Needing a little help, I have a customer wanting to make a small room 
> into a computer server room. One sprinkler in the room. Has anybody 
> used a solenoid valve, normally closed, and activated by a heat 
> detector? Trying to save the expense of a pre-action system.
>   DAVE GROVER
> Teem Sprinkler Co.
> Superintendent
> NFPA 25 Level II Inspector
> P 336-650-9005
> F 336-650-9007
> C 336-399-9006
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



-- 

*Damien Shannon*
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to