Matt,

Yes, that is basically it. Wood trusses, so bottom of trusses (ceiling) has the 
batt insulation, paper up.  We want to blow full of non-combustible insulation 
and not remove the paper-backed stuff.  It is a very large area, two accesses 
only, and a laborer would have to crawl through and remove it all.  Well, even 
to blow it full additional access locations would be necessary, but not as many 
as if that all has to come out.

Scott
 
Office: (763) 425-1001 x 2
Cell: (612) 759-5556

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise
Sent: Tuesday, June 30, 2015 7:52 AM
To: [email protected]
Subject: RE: Insulation and combustible concealed ceiling space

Am I picturing this correctly?

A lower level of wood 2x's with bat insulation directly on them (paper up), 
then laid on top of the paper (up to the top of  the space) is blown-in 
insulation?

If the paper is fully contained inside non-combustible insulation. 

1 - It seems unlikely that the paper could catch on fire or propagate fire 
across it. 
2 - this seems like the same idea that lets you exclude the rest of the 
combustibles (if the combustible surfaces are completely covered - then there 
are no exposed combustibles)

You could call it 2 separate combustible concealed spaces - one space below the 
paper, one space above the paper. Both spaces are completely filled with 
non-combustible insulation.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 
 
913.888.0647 ph 
913.888.0618 f 
913.526.7443 cell 
www. AFPsprink.com 
 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Scott A Futrell
Sent: Tuesday, June 30, 2015 7:34 AM
To: [email protected]
Subject: Insulation and combustible concealed ceiling space

Has anyone ever had an issue with a combustible concealed space that has one 
layer of kraft-faced batt insulation laying on the ceiling (kraft side up 
toward the sky) and then the remainder filled full of blown-in, non-combustible 
insulation and an AHJ saying the kraft-faced insulation had to be removed?  Or, 
conversely that the kraft-faced was acceptable.  This is fiberglass batt 
insulation, standard thickness for joists/studs with kraft backing.

I’d really like to hear arguments for 1) having to remove the kraft-faced and 
why, and 2) leaving it in place and why.  I want to leave it in place.

Thanks!

Scott Futrell



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to