Thanks Ron.

Agreed. Completely. That plus the information in 8.15.1.2.12 & 16 that Mr. 
Denhardt pointed out to me will be in the letter.

Scott

Office: (763) 425-1001 x 202
Cell: (612) 759-5556

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Tuesday, June 30, 2015 12:21 PM
To: [email protected]
Subject: Re: Insulation and combustible concealed ceiling space

Seems to me that the purpose of filled am otherwise combustible concealed space 
with a non-combustible material is to displace oxygen and so remove a leg of 
the triangle, or a facet of the tetrahedron if you prefer solid geometric 
models. Since the concealed space is already combustible due to the wood 
trusses, the addition of a layer of kraft paper sandwiched between a 
non-combustible batt and non-combustible blown in insulation will not 
spontaneously combust and burn on it's own. I can't think of why the AHJ would 
consider displacement of oxygen to work on keeping the wooden trusses from 
burning but not the paper.

On Tue, Jun 30, 2015 at 6:14 AM, Scott A Futrell <[email protected]> wrote:

> Matt,
>
> Yes, that is basically it. Wood trusses, so bottom of trusses 
> (ceiling) has the batt insulation, paper up.  We want to blow full of 
> non-combustible insulation and not remove the paper-backed stuff.  It 
> is a very large area, two accesses only, and a laborer would have to 
> crawl through and remove it all.  Well, even to blow it full 
> additional access locations would be necessary, but not as many as if that 
> all has to come out.
>
> Scott
>
> Office: (763) 425-1001 x 2
> Cell: (612) 759-5556
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Matt 
> Grise
> Sent: Tuesday, June 30, 2015 7:52 AM
> To: [email protected]
> Subject: RE: Insulation and combustible concealed ceiling space
>
> Am I picturing this correctly?
>
> A lower level of wood 2x's with bat insulation directly on them (paper 
> up), then laid on top of the paper (up to the top of  the space) is 
> blown-in insulation?
>
> If the paper is fully contained inside non-combustible insulation.
>
> 1 - It seems unlikely that the paper could catch on fire or propagate 
> fire across it.
> 2 - this seems like the same idea that lets you exclude the rest of 
> the combustibles (if the combustible surfaces are completely covered - 
> then there are no exposed combustibles)
>
> You could call it 2 separate combustible concealed spaces - one space 
> below the paper, one space above the paper. Both spaces are completely 
> filled with non-combustible insulation.
>
> Matt Grisé PE*, LEED AP, NICET II
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.526.7443 cell
> www. AFPsprink.com
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Scott A 
> Futrell
> Sent: Tuesday, June 30, 2015 7:34 AM
> To: [email protected]
> Subject: Insulation and combustible concealed ceiling space
>
> Has anyone ever had an issue with a combustible concealed space that 
> has one layer of kraft-faced batt insulation laying on the ceiling 
> (kraft side up toward the sky) and then the remainder filled full of 
> blown-in, non-combustible insulation and an AHJ saying the kraft-faced 
> insulation had to be removed?  Or, conversely that the kraft-faced was 
> acceptable.  This is fiberglass batt insulation, standard thickness 
> for joists/studs with kraft backing.
>
> I’d really like to hear arguments for 1) having to remove the 
> kraft-faced and why, and 2) leaving it in place and why.  I want to leave it 
> in place.
>
> Thanks!
>
> Scott Futrell
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to