It is required to furnish thrust restraint at mechanical joints.  Mechanical 
restraints and thrust blocks are both widely accepted forms of restraint, so 
either one is acceptable.   It is not required to furnish both, but I've seen 
many applications where both methods were used together for one reason or 
another.

Steve Leyton
Protection Design & Consulting





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Gerzayn Fuentes @ CEPI.MX
Sent: Thursday, July 16, 2015 10:47 AM
To: [email protected]
Subject: Thrust block vs Restrainers - Underground

Hello, folks!

I am working with underground pipe PVC DR14 C900 for a fire sprinkler system 
and I do understand that if we use restrainers (for example:
SIGMA PV-LOK-PVM and PVP) in/near the MJ fittings, we do not need to use thrust 
blocks. ¿Is this true?

I would appreciate if someone could share an Excel file to calculate the thrust 
block size.

Thanks

Best regards!
_______________________
Gerzayn Fuentes
CEPI - Mexico
T. + 52 (81) 1766-0800