Most jurisdictions (at least in Northern California) have their own specs on 
the required size of the thrust block and a few require a concrete thrust block 
regardless of the restraint used. I would check with the AHJ for 
clarification......

Rocci Cetani III, CET
Lead Designer
Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590
C- (408) 595-3906

[email protected]
www.norcalfire.com

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information 
belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Gerzayn Fuentes @ CEPI.MX
Sent: Thursday, July 16, 2015 10:47 AM
To: [email protected]
Subject: Thrust block vs Restrainers - Underground

Hello, folks!

I am working with underground pipe PVC DR14 C900 for a fire sprinkler system 
and I do understand that if we use restrainers (for example:
SIGMA PV-LOK-PVM and PVP) in/near the MJ fittings, we do not need to use thrust 
blocks. ¿Is this true?

I would appreciate if someone could share an Excel file to calculate the thrust 
block size.

Thanks

Best regards!
_______________________
Gerzayn Fuentes
CEPI - Mexico
T. + 52 (81) 1766-0800
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to