Ben,
Look at the Victaulic Sheet page 97 it states that they are UL Listed for 
branch connections, arm-overs,side-arms ( they must mean guns here) sprigs, 
drop nipples, and direct sprinkler head connections.Suitable hanger support of 
branch outlet should be considered to prevent Style 922 rotation.
Mike

> From: [email protected]
> Date: Wed, 30 Sep 2015 12:44:15 -0400
> Subject: Re: Hooklet tees
> To: [email protected]
> 
> Mike,
> 
> The AHJ is stating that the installation instructions say that they are not
> to be used for branch line outlets.
> I've always taken that to mean that you can't come off a main and feed
> multiple heads with one hooker.
> The AHJ's interpretation is that this means you cannot come off of a branch
> line with them... which makes no sense to anyone at my office.
> 
> Now, though, after reading the data sheet that Damien linked to, where is
> says that the strap tees are for heads, drops, or gauages, it makes me
> wonder if they don't have a valid point.
> http://www.vikinggroupinc.com/usrelated/vgs/V-723.pdf
> 
> We normally use Grinnell 40-5 strap tees, and they specifically say it can
> be used with full lengths of pipe...
> I've never heard before that you can't (or shouldn't) use strap tees for
> armovers.
> http://www.tyco-fire.com/TD_TFP/TFP/TFP1720_05_2015.pdf
> 
> Just as a backstory, this is an existing 10 story building that we're doing
> basically TFO work for on a few floors.  Another GC with another sprinkler
> contractor is doing another TFO on another floor in the building, and all
> four companies got put on email blast by the AHJ.
> 
> We are about done with our portion of the job, and the hooker fittings were
> basically used as WOLs for the shell spaces.  Our installers won't touch
> them, though, and we put it new mechanical tees if we need to reuse an
> outlet (or so I'm told)
> 
> 
> Benjamin Young
> 
> On Wed, Sep 30, 2015 at 12:20 PM, Mike Hairfield <[email protected]> wrote:
> 
> > They are Victaulic #922 Hooker Tees.
> > How does the AHJ know that they were not installed properly?
> > Mike
> >
> > > From: [email protected]
> > > Date: Wed, 30 Sep 2015 11:43:36 -0400
> > > Subject: Hooklet tees
> > > To: [email protected]
> > >
> > > Does anyone have any info on these?  I know our field guys call them
> > hooker
> > > tees, but searching for these things on google has been a minefield.
> > >
> > > Nothing on Victaulic's website...
> > >
> > > Just to be clear, I'm talking about the strap-style tee with the one-side
> > > cast 'hook' that goes around to the back of the piping with the snap-off
> > > lock bolt.
> > >
> > >
> > > I've always kind of treated them like FIT fittings or roustabouts:
> > > interesting concept, poor execution, and don't touch them if they're
> > > existing.
> > >
> > > We have an AHJ telling us that we have to replace them all on a tenant
> > > fit-out because they were not installed properly.
> > >
> > > Any help would be appreciated.
> > >
> > > Benjamin Young
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to