As promised, here's the datasheet for the Hooker fitting we got directly
from Victaulic... note the exact opposite wording from the one that Mike so
generously shared.
https://www.dropbox.com/s/h4yhc7a5v3vfvdi/1312_001.pdf?dl=0

We sent the 1988 install sheet to the fire marshal's office but haven't
heard back from them yet.


Benjamin Young

On Wed, Sep 30, 2015 at 2:05 PM, rongreenman . <[email protected]>
wrote:

> I think you're right and I think you'll find a lot of that in the industry
> where the stuff that was held close by a company seems to just disappear
> like it never existed.
>
> On Wed, Sep 30, 2015 at 10:54 AM, Ben Young <[email protected]>
> wrote:
>
> > So the data sheet that Victaulic sent our PM is just as Lamar said, for
> > heads, drops, gauges, etc. only.
> > But, that sheet's dated 1980, where the install manual from Mike is
> 1988...
> >
> > When i get a copy of the 1980 data sheet, I'll link it to you guys via
> > dropbox.  (PM keeps forgetting to send it to me)
> >
> > The Hooker fittings data seemingly all vanished into a black hole,
> because
> > you can barely find anything online, even with the proper information.
> The
> > only other sprinkler product I know of that's like that are Omega heads.
> > Its probably just a coincidence but my gut says these fittings must have
> > been a huge legal liability for the manufacturer.  At least with the
> Omegas
> > you can still see the CPSC website info and news reports, but there are
> no
> > datasheets or other catalog cuts available online open to the public.
> >
> >
> > Benjamin Young
> >
> > On Wed, Sep 30, 2015 at 1:29 PM, Mike Hairfield <[email protected]> wrote:
> >
> > > That's not what it says on the Victaulic Data sheet, want a copy?
> > >
> > >
> > > > Date: Wed, 30 Sep 2015 13:15:30 -0400
> > > > Subject: Re: Hooklet tees
> > > > From: [email protected]
> > > > To: [email protected]
> > > >
> > > > The "Hookers" were always intended for use installing sprinkler heads
> > > only.
> > > > As a short-cut, there were some contractors who took it a step
> further
> > > and
> > > > used them as you have stated, incorrectly.
> > > >
> > > > Lamar Vaughn
> > > >
> > > > On Wed, Sep 30, 2015 at 12:55 PM, Ben Young <
> [email protected]
> > >
> > > > wrote:
> > > >
> > > > > In deference to your 'side-arm' comment Mike, I'm going to give
> this
> > > to our
> > > > > PM and call it a smoking gun!
> > > > >
> > > > > Thanks again for your help and providing the sheet.
> > > > >
> > > > >
> > > > > Benjamin Young
> > > > >
> > > > > On Wed, Sep 30, 2015 at 12:52 PM, Mike Hairfield <[email protected]>
> > > wrote:
> > > > >
> > > > > > Ben,
> > > > > > Look at the Victaulic Sheet page 97 it states that they are UL
> > > Listed for
> > > > > > branch connections, arm-overs,side-arms ( they must mean guns
> here)
> > > > > sprigs,
> > > > > > drop nipples, and direct sprinkler head connections.Suitable
> hanger
> > > > > support
> > > > > > of branch outlet should be considered to prevent Style 922
> > rotation.
> > > > > > Mike
> > > > > >
> > > > > > > From: [email protected]
> > > > > > > Date: Wed, 30 Sep 2015 12:44:15 -0400
> > > > > > > Subject: Re: Hooklet tees
> > > > > > > To: [email protected]
> > > > > > >
> > > > > > > Mike,
> > > > > > >
> > > > > > > The AHJ is stating that the installation instructions say that
> > > they are
> > > > > > not
> > > > > > > to be used for branch line outlets.
> > > > > > > I've always taken that to mean that you can't come off a main
> and
> > > feed
> > > > > > > multiple heads with one hooker.
> > > > > > > The AHJ's interpretation is that this means you cannot come off
> > of
> > > a
> > > > > > branch
> > > > > > > line with them... which makes no sense to anyone at my office.
> > > > > > >
> > > > > > > Now, though, after reading the data sheet that Damien linked
> to,
> > > where
> > > > > is
> > > > > > > says that the strap tees are for heads, drops, or gauages, it
> > > makes me
> > > > > > > wonder if they don't have a valid point.
> > > > > > > http://www.vikinggroupinc.com/usrelated/vgs/V-723.pdf
> > > > > > >
> > > > > > > We normally use Grinnell 40-5 strap tees, and they specifically
> > > say it
> > > > > > can
> > > > > > > be used with full lengths of pipe...
> > > > > > > I've never heard before that you can't (or shouldn't) use strap
> > > tees
> > > > > for
> > > > > > > armovers.
> > > > > > > http://www.tyco-fire.com/TD_TFP/TFP/TFP1720_05_2015.pdf
> > > > > > >
> > > > > > > Just as a backstory, this is an existing 10 story building that
> > > we're
> > > > > > doing
> > > > > > > basically TFO work for on a few floors.  Another GC with
> another
> > > > > > sprinkler
> > > > > > > contractor is doing another TFO on another floor in the
> building,
> > > and
> > > > > all
> > > > > > > four companies got put on email blast by the AHJ.
> > > > > > >
> > > > > > > We are about done with our portion of the job, and the hooker
> > > fittings
> > > > > > were
> > > > > > > basically used as WOLs for the shell spaces.  Our installers
> > won't
> > > > > touch
> > > > > > > them, though, and we put it new mechanical tees if we need to
> > > reuse an
> > > > > > > outlet (or so I'm told)
> > > > > > >
> > > > > > >
> > > > > > > Benjamin Young
> > > > > > >
> > > > > > > On Wed, Sep 30, 2015 at 12:20 PM, Mike Hairfield <
> [email protected]
> > >
> > > > > wrote:
> > > > > > >
> > > > > > > > They are Victaulic #922 Hooker Tees.
> > > > > > > > How does the AHJ know that they were not installed properly?
> > > > > > > > Mike
> > > > > > > >
> > > > > > > > > From: [email protected]
> > > > > > > > > Date: Wed, 30 Sep 2015 11:43:36 -0400
> > > > > > > > > Subject: Hooklet tees
> > > > > > > > > To: [email protected]
> > > > > > > > >
> > > > > > > > > Does anyone have any info on these?  I know our field guys
> > call
> > > > > them
> > > > > > > > hooker
> > > > > > > > > tees, but searching for these things on google has been a
> > > > > minefield.
> > > > > > > > >
> > > > > > > > > Nothing on Victaulic's website...
> > > > > > > > >
> > > > > > > > > Just to be clear, I'm talking about the strap-style tee
> with
> > > the
> > > > > > one-side
> > > > > > > > > cast 'hook' that goes around to the back of the piping with
> > the
> > > > > > snap-off
> > > > > > > > > lock bolt.
> > > > > > > > >
> > > > > > > > >
> > > > > > > > > I've always kind of treated them like FIT fittings or
> > > roustabouts:
> > > > > > > > > interesting concept, poor execution, and don't touch them
> if
> > > > > they're
> > > > > > > > > existing.
> > > > > > > > >
> > > > > > > > > We have an AHJ telling us that we have to replace them all
> > on a
> > > > > > tenant
> > > > > > > > > fit-out because they were not installed properly.
> > > > > > > > >
> > > > > > > > > Any help would be appreciated.
> > > > > > > > >
> > > > > > > > > Benjamin Young
> > > > > > > > > _______________________________________________
> > > > > > > > > Sprinklerforum mailing list
> > > > > > > > > [email protected]
> > > > > > > > >
> > > > > > > >
> > > > > >
> > > > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > > > > > > >
> > > > > > > > _______________________________________________
> > > > > > > > Sprinklerforum mailing list
> > > > > > > > [email protected]
> > > > > > > >
> > > > > > > >
> > > > > >
> > > > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > > > > > > >
> > > > > > > _______________________________________________
> > > > > > > Sprinklerforum mailing list
> > > > > > > [email protected]
> > > > > > >
> > > > > >
> > > > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > > > > >
> > > > > > _______________________________________________
> > > > > > Sprinklerforum mailing list
> > > > > > [email protected]
> > > > > >
> > > > > >
> > > > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > > > > >
> > > > > _______________________________________________
> > > > > Sprinklerforum mailing list
> > > > > [email protected]
> > > > >
> > > > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > > > >
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
>
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to