It's possible the AHJ has accepted these to be of limited area if the
sub-systems serve less than 20 sprinklers.  NFPA offers multiple
solutions for "monitoring", including the locking of valves.  Perhaps
the AHJ approved an alternative to electronic supervision.   

Steve L.





-----Original Message-----
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
firs...@aol.com
Sent: Monday, October 05, 2015 7:38 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Monitoring 13D control valves in California 

The California Building Code requires sprinkler control valves to be
electrically monitored. One of the exceptions is One and Two Family
Dwellings, 13D.

What if it is a stand alone 13D system? (2" water meter with one DCVA to
a 2" underground, serving a row of 5 town homes with one hour
separations between units. The 2" underground branches off to each unit.
Each unit has it's own flow switch and test valve).

The exception specifically states for one and two family dwellings
because the control valve is before the domestic service so shutting off
the sprinklers shuts off the domestic therefor it is self monitoring.
The stand alone serving 5 units does not have this valve arrangement
therefore it would require electric monitoring per CBC.

Am I thinking correctly? According to CBC the two control valves on the
DCVA would need tampers, correct? 

Owen Evans

Sent from my iPad
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to