It appears that both the AHJ and contractor  have made mistakes on this 
project. I am interested in finding out what exactly happened. We should all 
play by the same rules. Im trying to figure out what is correct here according 
to standard, CFC & CBC. Like I said, it looks like a 13R but now they're saying 
its a 13D without DCVA monitoring. 

Sent from my iPhone

> On Oct 5, 2015, at 9:48 AM, Steve Leyton <st...@protectiondesign.com> wrote:
> 
> Are you doing a 3rd party inspection or some sort of risk management/loss 
> prevention analysis?  Why not just call the AHJ or installing contractor and 
> ask for approved basis of design?
> 
> SL
> 
> 
> -----Original Message-----
> From: Sprinklerforum on behalf of firs...@aol.com
> Sent: Mon 10/5/2015 9:37 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Monitoring 13D control valves in California 
> 
> Hi Steve, thanks for responding. Isn't the CBC more restrictive therefore you 
> can't allow something less? This particular system looks like a 13R but they 
> failed to provide electrical for tamper switches. So now they argue it is a 
> 13D serving a building with 5 townhouse's separated by 1 hour construction. 
> My thinking is since it is 5 units, not one or two family dwelling, the 
> exception for electrical monitoring does not apply. Therefore tampers are 
> required. Am I correct?   
> 
> Sent from my iPhone
> 
>> On Oct 5, 2015, at 8:52 AM, Steve Leyton <st...@protectiondesign.com> wrote:
>> 
>> It's possible the AHJ has accepted these to be of limited area if the
>> sub-systems serve less than 20 sprinklers.  NFPA offers multiple
>> solutions for "monitoring", including the locking of valves.  Perhaps
>> the AHJ approved an alternative to electronic supervision.   
>> 
>> Steve L.
>> 
>> 
>> 
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
>> firs...@aol.com
>> Sent: Monday, October 05, 2015 7:38 AM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: Monitoring 13D control valves in California 
>> 
>> The California Building Code requires sprinkler control valves to be
>> electrically monitored. One of the exceptions is One and Two Family
>> Dwellings, 13D.
>> 
>> What if it is a stand alone 13D system? (2" water meter with one DCVA to
>> a 2" underground, serving a row of 5 town homes with one hour
>> separations between units. The 2" underground branches off to each unit.
>> Each unit has it's own flow switch and test valve).
>> 
>> The exception specifically states for one and two family dwellings
>> because the control valve is before the domestic service so shutting off
>> the sprinklers shuts off the domestic therefor it is self monitoring.
>> The stand alone serving 5 units does not have this valve arrangement
>> therefore it would require electric monitoring per CBC.
>> 
>> Am I thinking correctly? According to CBC the two control valves on the
>> DCVA would need tampers, correct? 
>> 
>> Owen Evans
>> 
>> Sent from my iPad
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
>> .org
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to