So call the AHJ and ask for the basis of design.    

SL



-----Original Message-----
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
firs...@aol.com
Sent: Monday, October 05, 2015 10:44 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Monitoring 13D control valves in California 

It appears that both the AHJ and contractor  have made mistakes on this
project. I am interested in finding out what exactly happened. We should
all play by the same rules. Im trying to figure out what is correct here
according to standard, CFC & CBC. Like I said, it looks like a 13R but
now they're saying its a 13D without DCVA monitoring. 

Sent from my iPhone

> On Oct 5, 2015, at 9:48 AM, Steve Leyton <st...@protectiondesign.com>
wrote:
> 
> Are you doing a 3rd party inspection or some sort of risk
management/loss prevention analysis?  Why not just call the AHJ or
installing contractor and ask for approved basis of design?
> 
> SL
> 
> 
> -----Original Message-----
> From: Sprinklerforum on behalf of firs...@aol.com
> Sent: Mon 10/5/2015 9:37 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Monitoring 13D control valves in California
> 
> Hi Steve, thanks for responding. Isn't the CBC more restrictive
therefore you can't allow something less? This particular system looks
like a 13R but they failed to provide electrical for tamper switches. So
now they argue it is a 13D serving a building with 5 townhouse's
separated by 1 hour construction. My thinking is since it is 5 units,
not one or two family dwelling, the exception for electrical monitoring
does not apply. Therefore tampers are required. Am I correct?   
> 
> Sent from my iPhone
> 
>> On Oct 5, 2015, at 8:52 AM, Steve Leyton <st...@protectiondesign.com>
wrote:
>> 
>> It's possible the AHJ has accepted these to be of limited area if the

>> sub-systems serve less than 20 sprinklers.  NFPA offers multiple 
>> solutions for "monitoring", including the locking of valves.  Perhaps
>> the AHJ approved an alternative to electronic supervision.   
>> 
>> Steve L.
>> 
>> 
>> 
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
>> firs...@aol.com
>> Sent: Monday, October 05, 2015 7:38 AM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: Monitoring 13D control valves in California
>> 
>> The California Building Code requires sprinkler control valves to be 
>> electrically monitored. One of the exceptions is One and Two Family 
>> Dwellings, 13D.
>> 
>> What if it is a stand alone 13D system? (2" water meter with one DCVA

>> to a 2" underground, serving a row of 5 town homes with one hour 
>> separations between units. The 2" underground branches off to each
unit.
>> Each unit has it's own flow switch and test valve).
>> 
>> The exception specifically states for one and two family dwellings 
>> because the control valve is before the domestic service so shutting 
>> off the sprinklers shuts off the domestic therefor it is self
monitoring.
>> The stand alone serving 5 units does not have this valve arrangement 
>> therefore it would require electric monitoring per CBC.
>> 
>> Am I thinking correctly? According to CBC the two control valves on 
>> the DCVA would need tampers, correct?
>> 
>> Owen Evans
>> 
>> Sent from my iPad
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler
>> .org
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org