This is outside the purview of NFPA 13.

You're dealing with flammable and combustible liquids, hydrocarbons on which 
water alone will have limited affect.

For fuel loading/unloading stations it is common to employ foam-water deluge 
for the area below the canopy.  

Also an option is dry chemical.  Pyrochem has a system called ATTENDANT II 
(distributed by Tyco)

The HAJ would have to approve either one but more tend to lean towards a 
sprinklered solution than a one-shot gaseous system.  A very windy day could 
totally render a gaseous extinguishing system useless.

For design you do need to consider wind effect on your system discharge.  Don't 
get swayed into the minimum .16 gpm/sf permitted on foam-water systems.  You 
can have coverage issues again due to wind influences.  

NFPA 30, NFPA 30A, NFPA 16 and NFPA 2001 are good places to start.

Good luck and have fun!  

Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of James Crawford
Sent: Tuesday, December 08, 2015 1:04 PM
To: [email protected]
Subject: Canopies Over gads Pumps

Looking for some direction on the protection of a Gas Service station canopy 
over the gas pumps.

 

We have an AHJ that want the canopy protected, but I can't find anything that 
outlines the protection requirements for this area. My first thought is Extra 
Hazard group 1.

 

Can someone point me in the right direction

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  [email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to