Modeled:
(2) heat detectors, 8" below ceiling, 8" apart, with and without 12" deep
beam centered between them.

Results without--
Both near and far side heads activate at 90.5 seconds.
Margin of error a few tenths of a second.

Results with--
near side=93.8 seconds.
far side=115.0 seconds.
Same margin of error.

Head scratching --
1) I doubt in real life two heads 8" apart would activate within tenths of
a second of each other, my feel is more like a few, enough for one to
cold-solder the other.
2) in a model the spray pattern of a sidewall can be straight out, but in
real life I think enough would be splashed backward to cause 1).

For 30 years, if I thought beyond what the book said about max deflector
distance I thought "ok, the heat rises, hits the bottom of the deck, and
starts coming down, and when this heat gets, say, 12" down the head pops".
Well, 10 years ago I realized that that is normal-- and the emergency is
where the heated air is travelling horizontally five to ten feet per second
across the head.
10 years ago is also when I first heard "ceiling jet". I really resented a
Code Person telling me anything about sprinklers but, after 3 months of
getting my sprinkler (oops i mean head) around mass and the metric system
learning the first things about FDS, it started sinking in that the ceiling
jet is really where is at re: activation.

Brad C

Ps- this new thread is tied to the recent "can sidewalls..." thread.
Ps2- Ron, I'm not too sick, tired (or lazy), to look stuff up-- i just
don't have access to commentary, and I was curious, but it can wait.
Ps3- Ron2-----please don't be a stranger