Thanks Rahe.
Just to try to clarify, 13 shows sidewalls with a wall, or soffit, and
soffits normally protrude from a wall. Apparently some manufacturer's data
says they can be used with a wall or beam, but I doubt what was envisioned
was "back-to-back" sidewalls with a beam between them, which would be
required by 13 and the data, but likely a beam say, 8" from a "real wall",
and only on the interior side, to better look like the pictures in 13.
And please note, the activation times I showed really don't mean much-- I
used a space of X by Y by Z, open on the end opposite the fire, with a
certain heat release and fire growth rate. Changing any of those would
change the activation times.
The interesting thing is difference with and without the beam, and that is
what I meant by the margin of error being tenths of a second. In other
words, I don't try to predict anything, I like keeping all things the same
but one, say deflector distance, and seeing what the difference is,
according to the model that is :)

Brad
On Dec 31, 2015 12:06 PM, "Rahe Loftin - 7PMC" <[email protected]> wrote:

> I got it.  I was thinking that you had sidewalls 8 inches apart back to
> back and another set 8 feet from them.  Very interesting test.  It is
> always interesting to find things in NFPA 13 that mysteriously do not work,
> as indicated, in real life.
>
>
>
> *Success Through Code Compliance*
>
> *Rahe Loftin, PE  *
> *Regional Fire Protection Engineer*
> *General Services Administration*
> *Region 7 - TX, OK, NM, AR, LA*
> *Facilities Management & Support 7PMC*
> *c - 817-371-3102*
> *o - 817-978-7299*
>
> On Wed, Dec 30, 2015 at 1:04 PM, Brad Casterline <[email protected]>
> wrote:
>
> > Rhae,
> > No, 8" apart is correct. This is a continuation of the ~do sidewalls
> need a
> > wall discussion~ but I made it new because I don't know how to trim
> threads
> > using my phone.
> > Very interesting stuff.
> > When looking at activation only I use a heat detector because the same
> RTI
> > algorithm is used for upright, pendent, sidewall, and heat detector.
> > It is interesting to note that the 12" deep beam affects the near sprk
> like
> > an 18" draftstop affects a water curtain sprk-- it disrupts the heat
> flow,
> > delaying activation a few seconds. I think an 18" draft stop is used to
> > contain an 18" "build down" of 'cold smoke', per floor, when openings are
> > required to be protected.
> > On Dec 30, 2015 12:30 PM, "Rahe Loftin - 7PMC" <[email protected]>
> > wrote:
> >
> > > Brad,
> > > Should your post say 8' apart instead of 8"?
> > >
> > >
> > >
> > > *Success Through Code Compliance*
> > >
> > > *Rahe Loftin, PE  *
> > > *Regional Fire Protection Engineer*
> > > *General Services Administration*
> > > *Region 7 - TX, OK, NM, AR, LA*
> > > *Facilities Management & Support 7PMC*
> > > *c - 817-371-3102*
> > > *o - 817-978-7299*
> > >
> > > On Wed, Dec 30, 2015 at 11:07 AM, Brad Casterline <
> > [email protected]>
> > > wrote:
> > >
> > > > Modeled:
> > > > (2) heat detectors, 8" below ceiling, 8" apart, with and without 12"
> > deep
> > > > beam centered between them.
> > > >
> > > > Results without--
> > > > Both near and far side heads activate at 90.5 seconds.
> > > > Margin of error a few tenths of a second.
> > > >
> > > > Results with--
> > > > near side=93.8 seconds.
> > > > far side=115.0 seconds.
> > > > Same margin of error.
> > > >
> > > > Head scratching --
> > > > 1) I doubt in real life two heads 8" apart would activate within
> tenths
> > > of
> > > > a second of each other, my feel is more like a few, enough for one to
> > > > cold-solder the other.
> > > > 2) in a model the spray pattern of a sidewall can be straight out,
> but
> > in
> > > > real life I think enough would be splashed backward to cause 1).
> > > >
> > > > For 30 years, if I thought beyond what the book said about max
> > deflector
> > > > distance I thought "ok, the heat rises, hits the bottom of the deck,
> > and
> > > > starts coming down, and when this heat gets, say, 12" down the head
> > > pops".
> > > > Well, 10 years ago I realized that that is normal-- and the emergency
> > is
> > > > where the heated air is travelling horizontally five to ten feet per
> > > second
> > > > across the head.
> > > > 10 years ago is also when I first heard "ceiling jet". I really
> > resented
> > > a
> > > > Code Person telling me anything about sprinklers but, after 3 months
> of
> > > > getting my sprinkler (oops i mean head) around mass and the metric
> > system
> > > > learning the first things about FDS, it started sinking in that the
> > > ceiling
> > > > jet is really where is at re: activation.
> > > >
> > > > Brad C
> > > >
> > > > Ps- this new thread is tied to the recent "can sidewalls..." thread.
> > > > Ps2- Ron, I'm not too sick, tired (or lazy), to look stuff up-- i
> just
> > > > don't have access to commentary, and I was curious, but it can wait.
> > > > Ps3- Ron2-----please don't be a stranger
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > >
> > > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to