I got it.  I was thinking that you had sidewalls 8 inches apart back to
back and another set 8 feet from them.  Very interesting test.  It is
always interesting to find things in NFPA 13 that mysteriously do not work,
as indicated, in real life.



*Success Through Code Compliance*

*Rahe Loftin, PE  *
*Regional Fire Protection Engineer*
*General Services Administration*
*Region 7 - TX, OK, NM, AR, LA*
*Facilities Management & Support 7PMC*
*c - 817-371-3102*
*o - 817-978-7299*

On Wed, Dec 30, 2015 at 1:04 PM, Brad Casterline <[email protected]>
wrote:

> Rhae,
> No, 8" apart is correct. This is a continuation of the ~do sidewalls need a
> wall discussion~ but I made it new because I don't know how to trim threads
> using my phone.
> Very interesting stuff.
> When looking at activation only I use a heat detector because the same RTI
> algorithm is used for upright, pendent, sidewall, and heat detector.
> It is interesting to note that the 12" deep beam affects the near sprk like
> an 18" draftstop affects a water curtain sprk-- it disrupts the heat flow,
> delaying activation a few seconds. I think an 18" draft stop is used to
> contain an 18" "build down" of 'cold smoke', per floor, when openings are
> required to be protected.
> On Dec 30, 2015 12:30 PM, "Rahe Loftin - 7PMC" <[email protected]>
> wrote:
>
> > Brad,
> > Should your post say 8' apart instead of 8"?
> >
> >
> >
> > *Success Through Code Compliance*
> >
> > *Rahe Loftin, PE  *
> > *Regional Fire Protection Engineer*
> > *General Services Administration*
> > *Region 7 - TX, OK, NM, AR, LA*
> > *Facilities Management & Support 7PMC*
> > *c - 817-371-3102*
> > *o - 817-978-7299*
> >
> > On Wed, Dec 30, 2015 at 11:07 AM, Brad Casterline <
> [email protected]>
> > wrote:
> >
> > > Modeled:
> > > (2) heat detectors, 8" below ceiling, 8" apart, with and without 12"
> deep
> > > beam centered between them.
> > >
> > > Results without--
> > > Both near and far side heads activate at 90.5 seconds.
> > > Margin of error a few tenths of a second.
> > >
> > > Results with--
> > > near side=93.8 seconds.
> > > far side=115.0 seconds.
> > > Same margin of error.
> > >
> > > Head scratching --
> > > 1) I doubt in real life two heads 8" apart would activate within tenths
> > of
> > > a second of each other, my feel is more like a few, enough for one to
> > > cold-solder the other.
> > > 2) in a model the spray pattern of a sidewall can be straight out, but
> in
> > > real life I think enough would be splashed backward to cause 1).
> > >
> > > For 30 years, if I thought beyond what the book said about max
> deflector
> > > distance I thought "ok, the heat rises, hits the bottom of the deck,
> and
> > > starts coming down, and when this heat gets, say, 12" down the head
> > pops".
> > > Well, 10 years ago I realized that that is normal-- and the emergency
> is
> > > where the heated air is travelling horizontally five to ten feet per
> > second
> > > across the head.
> > > 10 years ago is also when I first heard "ceiling jet". I really
> resented
> > a
> > > Code Person telling me anything about sprinklers but, after 3 months of
> > > getting my sprinkler (oops i mean head) around mass and the metric
> system
> > > learning the first things about FDS, it started sinking in that the
> > ceiling
> > > jet is really where is at re: activation.
> > >
> > > Brad C
> > >
> > > Ps- this new thread is tied to the recent "can sidewalls..." thread.
> > > Ps2- Ron, I'm not too sick, tired (or lazy), to look stuff up-- i just
> > > don't have access to commentary, and I was curious, but it can wait.
> > > Ps3- Ron2-----please don't be a stranger
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to