Working on a project that we've installed Tyco attic heads and the GC has now 
gone in and added roughly several inches of spray on insulation. When I say 
roughly I mean roughly, the depth varies from 6" to 12" with no consistency 
what so ever. I've told them that most of the piping will have to be lowered to 
stay within the required clearances but I also think the insulation needs to be 
"shaved" to a smooth consistent finish, obviously that didn't go over so well. 
Since attic heads are considered extended coverage I think it's safe to assume 
they need to be installed per the requirements of NFPA as well, under a smooth 
flat surface. Am I missing something?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935