In other words, only where the intermediate members exceed 10" depth, will
it Maybe need a shave - a few inches deep by six feet long.
It is ludicrous to insist on some kind of insulation iso-surface for things
to work right!
On Mar 29, 2016 12:28 PM, "Brad Casterline" <[email protected]> wrote:

>
> It would only be a problem if the rafter depth plus gob depth exceeded
> deflector depth, so you're looking at 16" to 22" (6" variation, like you
> said).
>
> But in that regard, it is not an activation issue, it is only an
> obstruction issue.
> Shave it where necessary to not be an obstruction?
> On Mar 29, 2016 12:07 PM, "Brian Harris" <[email protected]>
> wrote:
>
>> Brad-
>> The real issue we're having is the haphazard way the sprayed on
>> insulation was installed, there's no way to establish minimum & maximum
>> deflector distances.
>>
>> Brian Harris, CET
>> BVS Systems Inc.
>> bvssytemsinc.com
>>
>>
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]] On Behalf Of Brad
>> Casterline
>> Sent: Tuesday, March 29, 2016 11:23 AM
>> To: [email protected]
>> Subject: RE: Tyco Attic Heads
>>
>> Nope. Smoothness above the sprinkler only affects activation times, and
>> the differences are only a few seconds.
>> Do you worry if the intermediate framing members are 2x4, 2x6, 2x8, or
>> 2x10 (a 6" variation)? Do you worry if they are perpendicular or  parallel
>> to the throw? No, because min deflector distance for back-to-back at the
>> peak is 16". This is to get the throw beneath the 'unsmoothness' of the
>> bottom of the deck.
>> The U.L. tests of Tyco BB heads 'started' with previously listed QR, EC
>> heads- only the Deflectors were changed, and the throw patterns at
>> different pressures were measured. They did that by not changing the bottom
>> of the deck or changing deflector distance, but by raising and lowering the
>> Floor :).
>>
>> And actually I think a little roughness at the bottom of the deck might
>> even enhance activation a bit-- but I am certainly no Sprinkler Scientist-
>> and the Modeling of BB heads activation and patterns I have done has been
>> rather coarse, i.e., quick and dirty ;)
>>
>> b
>> On Mar 29, 2016 9:46 AM, "Brian Harris" <[email protected]>
>> wrote:
>>
>> > I talked with tech support and while he wasn't too concerned about the
>> > roughness off the insulation he did agree the insulation needs to be
>> > "shaved" to a uniform depth to assure proper deflector distances.
>> >
>> > Brian Harris, CET
>> > BVS Systems Inc.
>> > bvssytemsinc.com
>> >
>> >
>> > -----Original Message-----
>> > From: Sprinklerforum [mailto:
>> > [email protected]] On Behalf Of Bruce
>> > Verhei
>> > Sent: Tuesday, March 29, 2016 10:44 AM
>> > To: [email protected]
>> > Subject: Re: Tyco Attic Heads
>> >
>> > I like Matt's advice. Tyco may have information from original test
>> series.
>> > Sometimes some of conditions are to meet extreme distance or a minimum
>> > available pressure.
>> >
>> > While I'd repeat that Tyco's comments would apply to this particular
>> > project only, could you post?
>> >
>> > Best
>> >
>> > Bruce
>> >
>> > > On Mar 29, 2016, at 06:41, Matt Grise <[email protected]> wrote:
>> > >
>> > > I would call tyco's technical hotline.
>> > >
>> > > Matt Grisé PE*, LEED AP, NICET II
>> > > Sales Engineer
>> > > Alliance Fire Protection
>> > > 130 w 9th Ave.
>> > > North Kansas City, MO 64116
>> > >
>> > > *Licensed in KS & MO
>> > >
>> > > 913.888.0647 ph
>> > > 913.888.0618 f
>> > > 913.526.7443 cell
>> > > www. AFPsprink.com
>> > >
>> > >
>> > >
>> > > -----Original Message-----
>> > > From: Sprinklerforum
>> > > [mailto:[email protected]] On Behalf Of
>> > > Brian Harris
>> > > Sent: Tuesday, March 29, 2016 8:40 AM
>> > > To: [email protected]
>> > > Subject: RE: Tyco Attic Heads
>> > >
>> > > "bounce..."
>> > >
>> > > Brian Harris, CET
>> > > BVS Systems Inc.
>> > > bvssytemsinc.com
>> > >
>> > > -----Original Message-----
>> > > From: Sprinklerforum
>> > > [mailto:[email protected]] On Behalf Of
>> > > Brian Harris
>> > > Sent: Tuesday, March 29, 2016 8:23 AM
>> > > To: [email protected]
>> > > Subject: Tyco Attic Heads
>> > >
>> > > Working on a project that we've installed Tyco attic heads and the
>> > > GC
>> > has now gone in and added roughly several inches of spray on insulation.
>> > When I say roughly I mean roughly, the depth varies from 6" to 12"
>> > with no consistency what so ever. I've told them that most of the
>> > piping will have to be lowered to stay within the required clearances
>> > but I also think the insulation needs to be "shaved" to a smooth
>> > consistent finish, obviously that didn't go over so well. Since attic
>> > heads are considered extended coverage I think it's safe to assume
>> > they need to be installed per the requirements of NFPA as well, under
>> > a smooth flat surface. Am I missing something?
>> > >
>> > > Brian Harris, CET
>> > > BVS Systems Inc.
>> > > Sprinkler Division
>> > > bvssystemsinc.com<http://bvssystemsinc.com/>
>> > > Phone: 704.896.9989
>> > > Fax: 704.896.1935
>> > >
>> > > _______________________________________________
>> > > Sprinklerforum mailing list
>> > > [email protected]
>> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>> > > kl er.org _______________________________________________
>> > > Sprinklerforum mailing list
>> > > [email protected]
>> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>> > > kl er.org _______________________________________________
>> > > Sprinklerforum mailing list
>> > > [email protected]
>> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>> > > kl
>> > > er.org
>> >
>> > _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> >
>> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> > er.org _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> >
>> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> > er.org
>> >
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to