"That's the way we've always done it." Realistically, this is the way other disciplines are broken out, any underground utility going into the building is stopped at the 5ft out mark on the Civil drawings and the discipline owning the system such as plumbing has to run from within the bldg. to the 5ft out mark and connect. FP just got lumped into that whole mess. Some of this has to do with the slab pour schedule as it's not uncommon for the slab work to be poured long before the overall site utility package is ready to be issued let alone completely installed. So the subs show up early to install their run-outs and stop 5ft out since that should clear any foundation work that would have to be done.
I join Steve in this issue. As a contractor I'd have to either contract with the utilities contractor to install and then test that last section or rent a backhoe and an operator and do it myself. That small of a purchase cost me more than it would have cost the contractor doing the remainder of the system. The other problem I had was with the UG contractor not properly testing and flushing his portion of the system which I had to connect to. Our current standard practice is for the civil design to include ALL the UG FP mains up to the face of flange at 1'-0" above finished floor. I've heard no complaints about this from the field. Reluctantly we have had some instances due to lease and property arrangements where the property boundaries were 5ft off the building wall so inside the 5ft belonged to the bldg. owner and outside the 5ft belonged to the developer so we had to show it split at that point. But that's rare. Craig L. Prahl Fire Protection Group Lead/SME CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29303 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Tuesday, March 29, 2016 4:13 PM To: [email protected] Subject: RE: UG 5 ft outside building No, there isn't and this is going to be my pet peeve until retirement. As a consulting and design firm we have some influence over how contracts get specified and broken out, so I have been trying for 20 years to change this practice but it's just insidious. The best way to get the UG all into one contract is to tell the owners that it's more expensive and there's greater liability if they split it at 5'-0 ... that's something they understand. Here in CA, because of code amendments there are only two ways to bring an UG into the building - either come out outside and penetrate the exterior wall above grade or sweep through the floor with a one-piece in-building riser. No joints are allowed under footings or slabs, this due to countless failures due to poor installation practices, absence of anti-corrosion preventative measures and threat of failure from earthquakes. Ironically, using the in-building riser creates more of a bias toward making the sweep and the connectin g piece part of the building system because the builder doesn't want that expensive stainless steel stub standing exposed while they build the building around it. We do succeed in getting the UG and Building Systems completely separated about 20-25% of the time, but standard industry practice is still heavily biased toward including the 5'-0 portion with the building. To the speculative comments about how we got to this practice, I don't believe it has to do with insurance (at least not directly) or union labor scope or politics - I think it's more along the lines of civil engineering scope going back to a time when sprinklers were not in the code. Often a building was required to be sprinklered outside of the work of the architectural team and jurisdictional permit process. If the owner decided to or their insurance mandated sprinklers, the civil engineer would show a fire service to 5'-0 and leave it for the deferred design/build contractor to pick it up from there. Hopefully, as 3rd party designers become more common and firms like mine are delivering more new projects to the market, this can be better coordinated between civil, architect and fire protection and a more logical scope and construction sequence will evolve. Steve L. -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Todd Williams Sent: Tuesday, March 29, 2016 1:00 PM To: [email protected] Subject: UG 5 ft outside building Is there a rational explanation why the sprinkler contractor should bring in the last piece of underground from 5 ft outside the building? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-608-4559 (cell) Sent using CloudMagic [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org