Steve, you are one hundred percent correct.

I'm glad I'm not the only this bothers.  I rant and rave about it frequently.

First of all, the UG contractor is not flushing and testing the main in 
accordance with NFPA 13 and 24 and then no one is testing that 5'-0" joint or 
the last 5'-0" horizontally, the elbow, or the spigot piece. 

No insurance involvement, then or now.

Scott
 
Office: (763) 425-1001 x 2
Cell: (612) 759-5556

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Tuesday, March 29, 2016 3:13 PM
To: [email protected]
Subject: RE: UG 5 ft outside building

No, there isn't and this is going to be my pet peeve until retirement.  As a 
consulting and design firm we have some influence over how contracts get 
specified and broken out, so I have been trying for 20 years to change this 
practice but it's just insidious.  The best way to get the UG all into one 
contract is to tell the owners that it's more expensive and there's greater 
liability if they split it at 5'-0 ... that's something they understand.   Here 
in CA, because of code amendments there are only two ways to bring an UG into 
the building - either come out outside and penetrate the exterior wall above 
grade or sweep through the floor with a one-piece in-building riser.   No 
joints are allowed under footings or slabs, this due to countless failures due 
to poor installation practices, absence of anti-corrosion preventative measures 
and threat of failure from earthquakes.  Ironically, using the in-building 
riser creates more of a bias toward making the sweep and the connectin
 g piece part of the building system because the builder doesn't want that 
expensive stainless steel stub standing exposed while they build the building 
around it.   We do succeed in getting the UG and Building Systems completely 
separated about 20-25% of the time, but standard industry practice is still 
heavily biased toward including the 5'-0 portion with the building.

To the speculative comments about how we got to this practice, I don't believe 
it has to do with insurance (at least not directly) or union labor scope or 
politics - I think it's more along the lines of civil engineering scope going 
back to a time when sprinklers were not in the code.   Often a building was 
required to be sprinklered outside of the work of the architectural team and 
jurisdictional permit process.   If the owner decided to or their insurance 
mandated sprinklers, the civil engineer would show a fire service to 5'-0 and 
leave it for the deferred design/build contractor to pick it up from there.  
Hopefully, as 3rd party designers become more common and firms like mine are 
delivering more new projects to the market, this can be better coordinated 
between civil, architect and fire protection and a more logical scope and 
construction sequence will evolve.

Steve L.




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Todd Williams
Sent: Tuesday, March 29, 2016 1:00 PM
To: [email protected]
Subject: UG 5 ft outside building

Is there a rational explanation why the sprinkler contractor should bring in 
the last piece of underground from 5 ft outside the building?

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to