I'm not sure about the anomaly guiding the design. We've had one 9/11 event
and got TSA. We had one guy with a shoe bomb and everyone gets to take
their shoes off. We have three thousand deaths a year fro fires, mostly in
SFDs, and we're told sprinkling is too expensive. We have a quarter million
os so smoking related deaths per year and subsidize the tobacco companies.
How much do we subsidize the airlines to pay for TSA so w can feel safe in
the safest mode of transportation, miles per person, we have?

On Tue, May 10, 2016 at 1:37 AM, Kenneth Berman <[email protected]>
wrote:

> consider a remote manual pull station to give enough volume of trim piping
> to allow for pressure drop , even if you only loose a few drops through the
> check valve, because of pressure loss in the supply piping. Loss of
> underground pressure resulted in a pressure drop, back through the priming
> line, that set off an open head AFFF system in a building of ink tanks in
> KY. The trim piping held such a small volume that a couple drops was enough
> for the reliable deluge valve to trip, when the underground pressure was
> returned. Reliable supplied us with a top of the line silicone spring
> loaded plug check valve and it still lost a few pounds. A remote manual
> pull at the tanks gave enough volume to maintain the pressure to keep the
> valve set-up. This problem showed up because the maintenance man was
> filling the underground lines utilizing the main electric pump to speed up
> filling time. The priming line couldn't repressurize the priming chamber
> fast enough to keep the valve "safe".
>
> On Mon, May 9, 2016 at 4:33 PM, <[email protected]> wrote:
>
>> If you have smoke detection you have an electrical interface with the
>> P.A. system, so the pull station could be electrical as well as you can by
>> a P.A. trim for electrical actuation.
>>
>> Also it's common for the electrician to install fire alarm and detection
>> components if there is not a specific fire alarm contractor.
>>
>> There's a lot of info missing but installing a manual pull at the riser
>> is for service work as well, makes it real easy to test the valve tripping
>> mechanisms to be sure everything works as it should from the mechanical
>> side of things.
>>
>> We might also assume that the installer is working from a set of plans
>> telling him where to install it, instead of him just arbitrarily putting it
>> wherever he felt like it.
>>
>>
>> Craig L. Prahl
>> Fire Protection Group Lead/SME
>> CH2M
>> 200 Verdae Blvd.
>> Greenville, SC  29607
>> Direct - 864.920.7540
>> Fax - 864.920.7129
>> CH2MHILL Extension  77540
>> [email protected]
>>
>>
>>
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]] On Behalf Of Charles
>> Thurston
>> Sent: Monday, May 09, 2016 5:24 PM
>> To: [email protected]
>> Subject: Re: Pre action pull station
>>
>> Hello Todd,
>>
>> Better question is WHY is an electrician installing something that is not
>> electrical?
>>
>>
>> > > 2007 NFPA 13, 7.3.1.2 The automatic water control valve shall be
>> > > provided with hydraulic, pneumatic, or mechanical manual means for
>> > > operation that is independent of detection devices and of the
>> > > sprinklers.
>>
>> Monday, May 9, 2016, 5:04:55 PM, you wrote:
>>
>> > It is interesting that an electrician is by default the one selecting
>> > the best location for a device that is only intended to be used during
>> > a fire. And only when the integrated system has failed, and fire has
>> > been burning for some time prior to FD arrival.
>>
>>
>> > So expect that smoke is accumulating in the building. Can FF's safely
>> > get to activating device, and recognize it once there?
>>
>>
>> > This assume the FD is trained well enough to recognize the situation
>> > and understand manually activating system will almost always be the
>> > highest suppression (water application) activity.
>>
>>
>> > Are there facilities that also have it in their fire watch plan to
>> > activate system when they know detection system is down?
>>
>>
>> > Does having a Journeyman A electrical card make you the best person to
>> choose location?
>>
>>
>> > Bruce Verhei
>>
>> > On May 9, 2016, at 13:18, Todd Williams <[email protected]> wrote:
>>
>>
>> > The electrician installed it at the riser and the client  asked if this
>> was correct.
>>
>>
>> > Todd G Williams, PE
>> > Fire  Protection Design/Consulting
>> > Stonington,  CT
>> > 860-535-2080 (ofc)
>> > 860-608-4559  (cell)
>>
>> > Sent using CloudMagic
>>
>> > On Mon, May 9, 2016 at 3:46  PM,             rongreenman . <
>> [email protected]> wrote:
>>
>> > Typically a valve at the rider. Are you looking for the manual
>> > release for a particular riser or a rule as to where it has to  be?
>>
>> > On Monday, May 9, 2016, Todd Williams  <[email protected]> wrote:
>>
>> >> ANy information on  location?
>>
>> >> Todd G Williams, PE Fire Protection  Design/Consulting Stonington, CT
>> >> 860-535-2080 (ofc) 860-608-4559  (cell) Sent using CloudMagic [
>> >> https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
>> >>  On Mon, May 9, 2016 at 3:13 PM, rongreenman .
>> >> <[email protected]>
>> >> wrote:
>> >> Typically they're part  of the listed trim package.
>>
>> >> On Monday, May 9, 2016,  <[email protected]> wrote:
>>
>> >> > 2007 NFPA 13,  7.3.1.2 The automatic water control valve shall be
>> >> > provided  with hydraulic, pneumatic, or mechanical manual means for
>> >> > operation that is independent of detection devices and of the
>> >> > sprinklers.
>> >> >
>> >> >
>> >> > Craig L. Prahl
>> >>  > Fire Protection Group Lead/SME
>> >> > CH2M
>> >> > 200  Verdae Blvd.
>> >> > Greenville, SC 29607
>> >> > Direct -  864.920.7540
>> >> > Fax - 864.920.7129
>> >> > CH2MHILL  Extension 77540
>> >> > [email protected]  <javascript:;>
>> >> >
>> >> >
>> >> >
>> >> >  -----Original Message-----
>> >> > From: Sprinklerforum  [mailto:
>> >> > [email protected]  <javascript:;>] On
>> >> > Behalf Of Todd Williams
>> >> >  Sent: Monday, May 09, 2016 2:33 PM
>> >> > To:  [email protected] <javascript:;>
>> >> >  Subject: Pre action pull station
>> >> >
>> >> > I'm looking for  guidelines for manual pull stations on pre-action
>> >> systems.
>> >>  > Any idea where they are?
>> >> >
>> >> > Todd G Williams, PE  Fire Protection Design/Consulting Stonington,
>> >> > CT
>> >> > 860-535-2080  (ofc) 860-608-4559 (cell) Sent using CloudMagic  [
>> >> >
>> >>
>> >> https://secure-web.cisco.com/1Kt0u0GJLzxwwb7MCDiEPqnzAIXRuh45mBuCy231
>> >> KCQjUADAmsbstorfcS2u3cmf6VWoWnAPNKp1CfWgx57bhXLRwziiio3szpVlEoirXjlRl
>> >> aErxlmvOu9DRsancbU-wiLuZyxJzb9c-_ux8HhslMBhQAOxR32puEEiFLLjijqv9fIICy
>> >> _QU3maQJSPCR-iLU5CnzUTUvoxXYCJxJwTjbzkG_0V3gb-9cVyCd-xzc-L8H0xmaKv7fb
>> >> QWffYiW3G6xSDLbfEVTL3ngXgWNMUiUUNOy2UamgyBurOD7v2Wt9I-zYfsXH7PVWqALSf
>> >> RsvE3Rf_lEI6FNrK4RvyxIQd0B8-EQlft0ObsBsbh3PfyC9LvGZtVQnopiXWExly-erED
>> >> 5q-PLKR67YG4Se_JKujfY-IlabVTdjbDhH2DKOjWuzUFHnWAYGtth_N5_OKKm0kwtOJsC
>> >> CikyFoSnFz1Cgak_Q/https%3A%2F%2Fcloudmagic.com%2Fk%2Fd%2Fmailapp%3Fct
>> >> %3Dti%26cv%3D6.0.64%26pv%3D8.2%5D  >
>> >> _______________________________________________
>> >> >  Sprinklerforum mailing list
>> >> >  [email protected] <javascript:;>
>> >>  >
>> >> >
>> >>
>> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> >> ler.org
>> >>  >
>> >> > _______________________________________________
>> >>  > Sprinklerforum mailing list
>> >> >  [email protected] <javascript:;>
>> >>  >
>> >> >
>> >>
>> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> >> ler.org
>> >>  >
>>
>>
>> >> --
>> >> Sent from Gmail Mobile
>> >>  -------------- next part -------------- An HTML attachment was
>> >> scrubbed...
>> >> URL: <
>> >>
>> >> http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkl
>> >> er.org/attachments/20160509/ea1fbf6a/attachment.htm
>> >>  >
>> >> _______________________________________________
>> >>  Sprinklerforum mailing list
>> >>  [email protected]
>>
>> >>
>> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> >> ler.org
>> >>  -------------- next part -------------- An HTML attachment was
>> >> scrubbed...
>> >> URL: <
>> >>
>> >> http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkl
>> >> er.org/attachments/20160509/7e6e19c7/attachment.htm
>> >>  >
>> >> _______________________________________________
>> >>  Sprinklerforum mailing list
>> >>  [email protected]
>>
>> >>
>> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> >> ler.org
>>
>>
>>
>> > --
>> > Sent from Gmail Mobile
>> > -------------- next part -------------- An  HTML attachment was
>> > scrubbed...
>> > URL:
>> > <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkl
>> > er.org/attachments/20160509/6f8d881a/attachment.htm>
>> > _______________________________________________
>> > Sprinklerforum  mailing  list
>> > [email protected]
>> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> > er.org
>>
>> >
>>
>> > _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> > er.org
>>
>> >
>>
>>
>>
>> --
>> Best regards,
>>  Charles                            mailto:[email protected]
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>


-- 
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected]

253.576.9700

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to