Craig – the best way to distinguish a fire alarm pull station from a manual 
release station is though very clear signage.  If the risk associated with 
tripping the suppression system is big (as it often is – e.g. foam onto 
aircraft, expensive gas into room, etc.) then you can do a number of things, 
including: different colored releasing station from the fire alarm pull 
station; plastic cover over the releasing station; large fluorescent yellow 
sign above and/or around the releasing station with its purpose in large (3”) 
red letters; or any number of similar solutions. The point is that you’re right 
– in an emergency it’s hard to tell the difference so make it abundantly clear 
to the panicked individual. The small lettering on the releasing station itself 
won’t cut it in an emergency.

-------------------
How would you distinguish a fire alarm pull station at an egress path from a 
system actuation manual pull station?  In an emergency what person is going to 
stop to read and figure out which one does what?


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>


Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
KFIengineers.com<http://www.kfiengineers.com>

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to