I’m specifically referring to manual pull stations for preaction systems 
(thread) as well as other fire suppression systems (clean agents and kitchen), 
and the location of those pull stations.  The question from SL was where does 
it say to put them and the place I am aware of that provides some direction is 
NFPA 72.

Scott

Office: (763) 425-1001 x 2
Cell: (612) 759-5556

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Tuesday, May 10, 2016 4:51 PM
To: [email protected]
Subject: RE: Pre action pull station

I think people are getting different types of pull stations used for different 
functions confused when it comes to what is required when and where.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Scott Futrell
Sent: Tuesday, May 10, 2016 5:42 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Pre action pull station

It is not uncommon to have a manual pull station for fire suppression alongside 
an abort switch (button) for the same system with proper signage above both.

Scott

Office: (763) 425-1001 x 2
Cell: (612) 759-5556