Good morning Brian,

I suggest taking a look at section A.8.10.7.1.5. Here is a part of that
section:

*The last option should be putting sprinklers on the wall back behind the
face of the*
*cabinet because this location is subject to being blocked by*

*items placed on top of the cabinets.*

Juan

On Thu, Jul 7, 2016 at 8:15 AM, Mark Phillips <[email protected]>
wrote:

> The soffit would need to be flush with cabinet face  8.10.7.1.5.2 of NFPA
> 13 2010 ed in my opinion.
>
> Mark
>
>
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Brian
> Harris
> *Sent:* Thursday, July 07, 2016 11:06 AM
> *To:* [email protected]
> *Subject:* Obstructions Below Sidewall Sprinklers
>
>
>
> Looking for some clarification on sidewall sprinklers; We have a
> residential project that has a recessed sidewall head in the kitchen wall
> located 18” above a kitchen cabinet, the cabinet projects out 12” from the
> wall. Is this acceptable or does a soffit need to be built above the
> cabinet to bring the face of the sprinkler flush with the face of the
> cabinet?
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> Sprinkler Division
>
> bvssystemsinc.com
>
> Phone: 704.896.9989
>
> Fax: 704.896.1935
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>


-- 
Juan Munguia

[image: Thorpe Design Inc – Fire Sprinkler Systems]

C 209-380-0599
O 925.634.5758
F 925.634.5975
E [email protected]
W www.thorpedesign.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to