Its not required and explained by 8.10.7.1.5.2 From: Sprinklerforum [mailto:[email protected]] On Behalf Of Cliff Whitfield Sent: Thursday, July 07, 2016 11:21 AM To: [email protected] Subject: RE: Obstructions Below Sidewall Sprinklers
How do you address the 12" wide space that the wall cabinet creates between the top of the base cabinets and the bottom of the wall cabinets? It's not protected in either scenario. Cliff From: Sprinklerforum [mailto:[email protected]] On Behalf Of Mark Phillips Sent: Thursday, July 07, 2016 11:15 AM To: [email protected]<mailto:[email protected]> Subject: RE: Obstructions Below Sidewall Sprinklers The soffit would need to be flush with cabinet face 8.10.7.1.5.2 of NFPA 13 2010 ed in my opinion. Mark From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Thursday, July 07, 2016 11:06 AM To: [email protected]<mailto:[email protected]> Subject: Obstructions Below Sidewall Sprinklers Looking for some clarification on sidewall sprinklers; We have a residential project that has a recessed sidewall head in the kitchen wall located 18" above a kitchen cabinet, the cabinet projects out 12" from the wall. Is this acceptable or does a soffit need to be built above the cabinet to bring the face of the sprinkler flush with the face of the cabinet? Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org