I thought about writing a code change proposing fast response heads for spray 
booths. I was expressly interested in sprinklered booths in unsprinklered 
buildings. . 
A friend at FM forwarded several fire reports. Systems varied from several 
heads to the 50-60. 
Consistent was that all heads in space, and exhaust operated. And, except for 
remote supplied paint, fire was successfully contained to booth.
In addition someone at FM had done a report that stated that due to small, 
confined area, ceiling temps rose fast enough that the faster response heads 
would only operate something near ten seconds faster. I don't remember the 
model fire. This was specifically considering paper bag covered heads.
Quick response heads at the time were still a considerable margin over  
standard response. 
Given that they also tend to be a little more fragile, think changing covers, 
with minimal benefit, I walked away from pursuing it further.
Two things of note. This was before downdraft or semi-downdraft booths were 
common.
Booths with bulk tank or 55-gallon drum supplied, production spray operations 
did have failures. Fire caused failure of hose in booth. Pressure sensor 
commanded pump to supply more paint. Entire volume pumps into space. Not clear 
if this was flowing, or spraying, atomized faults. The two examples they had 
were in sprinklered buildings. A bunch of ceiling sprinklers in the shell 
buildings operated and controlled the fires.
Best
Bruce  Verhei
On Aug 8, 2016, at 17:17, Brad Casterline <[email protected]> wrote:

Shakey ground is all i have ever known Ken. 

I am no more a professional than you are.

THINK MAN!

small spaces with fast fires need the fastest acting sprinklers we can muster.

I've been in court myself a couple times- neither one over sprinklers though--

please stop being so stodgy!
On Aug 8, 2016 7:05 PM, "Parsley Consulting" <[email protected]> wrote:

  
    
  
  
    I don't know, Brad. 
        You're standing on pretty shaky ground there. 

        

        The decision to use QR sprinklers in an extra hazard occpuancy
        is a direct contradiction to 8.4.1.1.2 of NFPA 13, including the
        2016 edition, or a similar section number, at least as far back
        as the 1999 edition.  If you install QR sprinklers in a space
        that is legitimately classed as an extra hazard occupancy,
        aren't you directly contradicting this particular section of
        NFPA 13?  The handbook provides the following explanatory text
        on the topic:

      
    Extra
          hazard occupancies are characterized by the probability of
          fast-developing fires with high heat release rates that have
          the potential to open a large number of quick-response
          sprinklers before the sprinklers have time to control the
          fire. The operation of a large number of sprinklers in a
          relatively short time period has the potential to overtax the
          system. For this reason, quick-response sprinklers using the
          area

          design method of Chapter 11 are not permitted for the
          protection of extra hazard occupancies. Additional perspective
          on this can be found in the discussion of safety margin found
          in B.2.1.

    
    Further, I'm not aware
        of any QR sprinkler which has been tested and listed by an NRTL
        for use in protecting extra hazard occupancies.  Barring that,
        to follow the guidance you're suggesting the
        contractor/designer/installer has to violate both NFPA 13 AND
        the listing of the sprinkler.  I'm not suggesting the gloom and
        doom drama of "people could die", however it does concern me
        greatly when I read suggestions to ignore both texts. 

        

        My thought about that is to make sure your insurance is paid up,
        and have a good lawyer on retainer.  I don't know of a good
        defense while sitting in the witness chair to a question similar
        to, "Are you telling me you ignored the applicable law and the
        manufacturer's recommendations for the installation of that
        sprinkler?"  

        

        When I have nightmares I think about having to answer questions
        similar to that.

      
    Ken Wagoner,
          SET

          Parsley Consulting

          350 West 9th Avenue, Suite 206

            Escondido, California 92025

            
            Phone 760-745-6181

            
            Visit our
              website
          
    

      On 08/08/2016 4:17 PM, Brad Casterline wrote:

    
    
      We're not suppose to use QR in EH either but I say
        balderdash.

        That is for big open spaces beacase you could have a bunch of
        heads going off way over there when the emergency is way over
        here. Small spaces with fast fires are better off if you use low
        temp qr and calc every head possible going off
      

    
    

  


_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________