The reason for that is that manufacturers have not tested or had tested their 
SW sprinklers in the myriad of extra hazard applications therefore they are not 
listed for EH occupancies.

As far as ductwork, why anyone would use a SW is questionable.  Typically 
pendants are used as you don’t need the throw distance of a SW inside a piece 
of duct.

I would really question the designer on the design and reject it if I was 
reviewing.

Flexhead has a great system for ductwork, makes installation simple and is 
designed for this specific application.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Zachary Siegrist
Sent: Monday, August 08, 2016 6:02 PM
To: [email protected]
Subject: Paint spray application [EXTERNAL]

I was taught that sidewall sprinklers cannot be used in an extra hazard 
application.  At least that is what I recall.  Additionally, the protection 
areas and maximum spacing table for sidewall heads do not have any information 
for extra hazard occupancies. I am reviewing a set of plans for a paint spray 
booth and sprinklers must be spaced in ducts at 12 foot intervals.  The 
designers called out sidewall sprinklers on plans.  How is this best 
accomplished if you can't use sidewall sprinklers?

Zach