Pete,
I am wondering why you said,  "elect to follow the 5 year requirement"? I
thought it was required.

Joe

On Tue, Sep 6, 2016, 12:13 PM Larrimer, Peter A <[email protected]>
wrote:

> Let there be no doubt that the change was not done “seemingly
> unintentional”, but was done with keen intent in NFPA 25.  Take a look at
> the Report on Comments (ROC) for the 2011 edition of NFPA 25 and you will
> see that a “system” was purposely redefined in NFPA 25 even though the
> definition as reworded would not agree with what was in NFPA 13.
> http://www.nfpa.org/assets/files/AboutTheCodes/25/25-A2010-ROC.pdf
>
>
>
> Take a look at 25-104 and 25-187 in the link above.  Note the
> contentiousness of the issue based on the votes..
>
>
>
> Jody Massey (Joe) is right on target with his comments below.  The new
> definition provides no (or negative) fire protection system benefits with
> significant costs to the system owners who elect to follow the 5-year
> requirement.
>
>
>
> *Submitter: *Terry L. Victor, Tyco/SimplexGrinnell
>
> *Comment on Proposal No: *25-187
>
> *Recommendation: *New and revise text to read as follows:
>
> Incorporate the following changes as follows and renumber the entire
> chapter
>
> as shown:
>
> 14.1 General.
>
> This chapter shall provide the minimum requirements for conducting
>
> investigations of fire protection system piping for possible sources of
> materials
>
> that could cause pipe blockage.
>
> *14.1.1* For the purposes of this chapter a system shall consist of a
> shut-off*
>
> *valve, a water flow alarm device, a drain, and a check valve, alarm
> valve, dry*
>
> *pipe valve, deluge valve or preaction valve.*
>
> *A.14.1.1 A subdivision of a system does not necessarily require a
> separate*
>
> *obstruction investigation. In high-rise buildings, if each individual
> floor does*
>
> *not have a check valve in addition to the floor control valve, this
> piping does*
>
> *not need to be considered a separate system.*
>
> 14.2* Obstruction Investigation and Prevention Inspection
>
> 14.2.1 *Except as discussed in 14.2.1.1 and 14.2.1.3 *an inspection ….
>
> 14.2.1.1 Alternative ….
>
> 14.2.1.2 Tubercules or slime….
>
> *(New from ROP) 14.2.1.3 CPVC Pipe shall not be required to be*
>
> *inspected internally.*
>
> *(New from ROP) 14.2.1.4 In dry pipe systems and pre-action systems,*
>
> *the sprinkler removed for inspection shall be from the most remote branch*
>
> *line from the source of water that is not equipped with the inspectors
> test*
>
> *valve.*
>
> *(New from ROP) 14.2.1.5*Inspection of a cross main is not required*
>
> *where:*
>
> *(a) system piping is not accessible*
>
> *(b) system does not have a means of inspection such as grooved couplings*
>
> *or flushing connections*
>
> *(New from ROP) A.14.2.1.5 The inspection of piping is not required*
>
> *where the pipe is not readily accessible such as above gypsum ceilings.*
>
> *Additionally, not all systems, such as those installed in accordance with*
>
> *NFPA 13R, have flushing connections.*
>
> 14.3 Obstruction Investigation
>
> 14.2.2 3.1* An obstruction investigation …..
>
> 14.2.3 3.2* Systems …..
>
> 14. 2.3 3.2.1 If the condition …..
>
> 14. 2.3 3.2.2 Internal inspections …..
>
> 14. 2.3 3.2.3 Alternative …..
>
> 14.2.4 3.3* If an obstruction investigation …..
>
> 14.3 4 Ice Obstruction. Dry pipe.....
>
> 14.3 4.1 Alternative …..
>
> 14. 3 4.2 All penetrations …..
>
> *Substantiation: *Several changes were made to this chapter during the ROP
>
> that helped clarify the intent of some of the requirements in this chapter.
>
> However, there is still confusion on the difference between an obstruction
>
> inspection and an obstruction investigation. This confusion can be
> eliminated
>
> by separating these requirements and renumbering the chapter as shown.
> There
>
> also needs to be clarification on the definition of a system as it applies
> to this
>
> chapter.
>
> *Committee Meeting Action: Accept in Principle in Part*
>
> *Committee Statement: *Committee Action on Comment 25-76 (Log #CC4)
>
> addresses this issue.
>
> *Number Eligible to Vote: 30*
>
> *Ballot Results: *Affirmative: 22 Negative: 7
>
>
>
> Pete
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *rongreenman
> .
> *Sent:* Friday, September 02, 2016 11:25 AM
> *To:* [email protected]
> *Subject:* [EXTERNAL] Re: 5 year fire sprinkler Obstruction Assessment -
> What items in asystem define it as a separate wet pipe system?
>
>
>
> "*The problem being that someone changed something in the code and they
> "seemingly unintentionally" changed the definition (in loose terms) of a
> wet system:*
>
> from: a riser
>
> to: a riser, and each floor with a floor controller. "
>
>
>
> Never happened. Look at the definition of riser in 13. It still just says
> "The VERTICAL" supply piping in a sprinkler system." (13:13-3.5.9) If you
> look up the definition of sprinkler system in 13 you'll find floor control
> valves still don't define a system.
>
>
>
> *The actual problem being that someone that someone at NFSA interpreted
> something to mean something when a zillion other references throughout the
> book dispute that interpretation.* This thread seems to have become
> FaceBookish wherein someone says a thing and because that someone is
> perceived as an authority the comment the equivalent of a Supreme Court
> decision. No matter how many bloggers keep telling me Obama is coming to
> take my pistol I still seem to have it. Maybe he hasn't gotten to the NW
> yet.
>
>
>
> And Brad. If you've never read 25, but only 13A, do you even get an
> opinion? I read Zen and the Art of Motorcycle Mechanics and it didn't say a
> damned thing about repairing motorcycles.
>
>
>
> On Fri, Sep 2, 2016 at 6:01 AM, Brad Casterline <[email protected]>
> wrote:
>
> Thanks Joe, I appreciate you sharing your experience with NFPA 25.
>
> I've got my hands full trying to apply 13 right!
>
> Good luck- hopefully you will continue to get feedback from the heavy
> lifters.
>
>
>
> here is what I was looking for:
>
>
>
> "You do not do it for cpvc."
>
>
>
> Thanks again,
>
>
>
> Brad
>
>
>
>
> ------------------------------
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Jody Massey
> *Sent:* Friday, September 02, 2016 7:24 AM
> *To:* [email protected]
> *Subject:* Re: 5 year fire sprinkler Obstruction Assessment - What items
> in asystem define it as a separate wet pipe system?
>
>
>
> Brad,
>
> What I am now very clear on - is that I have stumbled into a hornets nest
> - with no hard answer.
>
>
>
> *The problem being that someone changed something in the code and they
> "seemingly unintentionally" changed the definition (in loose terms) of a
> wet system:*
>
> from: a riser
>
> to: a riser, and each floor with a floor controller.
>
>
>
> Just because there is a "seemingly unintentionally" change, does that mean
> we change how we do business - whatever the concequence?
>
>
>
> *This only effects every 5 year inspection for every large building in the
> USA. No big deal. *
>
>
>
> *Implication for obstruction assessment:*
>
>  X- story building with a three wet risers
>
> 1st scenario: look at 2 sprinkler heads
>
> 2nd scenarion: look at 3 sprinkler heads every 2 floors
>
>
>
> I am seeing people across the country "skipping" this part of the 5 year -
> and the AHJ not catching it - because it is costing in the neighborhood of
> $18k for a 5 year inspection because of misunderstanding.
>
>
>
> I do not have a problem with people spending money to keep the building
> safe, but there is another side to the coin.
>
>
>
> The commitee on the code (or wheover it is) debates each time on how often
> to open the system and look because when you do that, you introduce air.
> They are really worried about this and are trying to minimize this -
> because it can do more harm than good.
>
>
>
> If we look at a lot more heads just to meet the letter of the new
> "seemingly unintentional consequence of a code change" we:
>
>    1. get a better sample
>    2. charge the building alot more money
>    3. put the building at more risk
>    4. probably go against the intention of the people who write the code
>
> I dunno what to do... (insert head scratch here)
>
>
>
>
>
> And Brad - I am not a scholar on this stuff so I am probably wrong - but
> it is my understanding that you do this for all systems - not just wet. You
> look at *every* non-wet system plus *every other* wet system. The
> reasoning seems to be that dry systems will have a little water in there
> and lots of air which is a higher risk for growth. You do not do it for
> cpvc.  It just states you are looking for "The presence of sufficient
> foreign organic or inorganic material", if you find enough material, then
> you have a field day looking all over the building because you have entered
> the NFPA 25 14.3 zone.
>
>
>
> *- Joe*
>
> ᐧ
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
>
>
> --
>
> Ron Greenman
>
>
> 4110 Olson Dr., NW
> Gig Harbor, WA 98335
>
> [email protected]
>
> 253.576.9700
>
>
>
> The Universe is monstrously indifferent to the presence of man. -Werner
> Herzog, screenwriter, film director, author, actor and opera
> director (1942-)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to