Don't think I clearly stated my point but writin never been my best subject lol

Jeff
JB Fire Protection
Sent from my iPhone

> On Sep 1, 2016, at 11:49, Steve Leyton <[email protected]> wrote:
> 
> Uhhhhhh … not sure those metrics matter or if I even understand the point 
> you’re making.   
>  
> Once upon a time, floor controls were not required on multi-story buildings 
> unless subject building was code-classified as high-rise.  Even then, the 
> requirement to control and alarm each floor separately was (and still is) in 
> the building code(s) and we just played along.   Since those days, we now 
> have indoor plumbing AND clear prescriptions in NFPA 13 and 14 for when and 
> how to sectionally control floors of a sprinkler system.  But it’s still just 
> one system with a single main riser unless there’s more than one main riser.  
>  There is no limit to the number of standpipes you can install off of a 
> single “system”, but if you have floors greater than 52,000 sq. ft. in LH 
> and/or OH occupancies, then you would need two sprinkler risers or “systems”. 
>   Where it gets confusing to me is whether you can select two standpipes in a 
> single system (as defined by NFPA 14) and make them combination to fulfill 
> the requirement, or whether you would need a completely separate system with 
> its own connection to a water supply and dedicated riser.  
>  
> Perhaps someone can enlighten me, but it appears that the 2013 requirement 
> for floor control assemblies in buildings 2-stories in height has been taken 
> out of the standard.  So I guess the status quo in 13 depends on which 
> edition you’re using, but in a non-high-rise building, NFPA 14 affords you 
> the option of creating combination standpipes but requires that for every 
> sprinkler connection there must be a control and check valve.  So except for 
> the requirement to sectionally alarm each floor as in a high-rise, you have a 
> defacto floor control assembly in practice.   However, none of this creates a 
> separate “system” horizontally, IMHO.
>  
> The foregoing is my opinion only and is not intended to represent the NFPA 14 
> Technical Committee, nor serve as an interpretation of the standard.
>  
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>  
>  
>  
>  
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Jeff Bridges
> Sent: Thursday, September 01, 2016 11:31 AM
> To: [email protected]
> Subject: RE: 5 year fire sprinkler Obstruction Assessment - What items in a 
> system define it as a separate wet pipe system?
>  
> I didn’t
> I was showing if it all is one system as Ron was eluding to, floor controls 
> not considered as separation, the cumulative total of floor space being 
> covered under a single riser would be 120K
> BUT if floor controls ARE considered as a riser, each RISER is covering 30K.
> I never said that 30K is a max per riser but if, under my example, floor 
> controls are merely considered making the system easier to drain and not a 
> separate system, then it exceeds 52K as allowed.
> Right?
>  
> Jeff Bridges
> JB Fire Protection Inc
> (888) 523-4737 Fax (714) 578-0901
> Fire Sprinklers Save Lives & Property
> www.jbfireprotection.com
>  
> This email transmission (and any of its attachments) is intended only for the 
> person or entity to whom it is addressed, and may contain confidential, 
> proprietary and/or privileged information. No waiver of any applicable 
> privileges or protections is intended hereby. If you are not the person to 
> whom this transmission is addressed, you are hereby notified that the 
> disclosure, copying, distribution, reliance upon or use of any of the 
> information contained in this transmission is strictly prohibited. If you 
> have received this transmission in error, delete any copies which may exist 
> on your system and notify the sender immediately. This email transmission 
> cannot be guaranteed secure or error-free. Any views expressed in this 
> message are those of the individual sender, except where the sender specifies 
> them to be the views of the company and is authorized to do so.
>  
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Parsley Consulting
> Sent: Thursday, September 01, 2016 11:07 AM
> To: [email protected]
> Subject: Re: 5 year fire sprinkler Obstruction Assessment - What items in a 
> system define it as a separate wet pipe system?
>  
> Jeff,
>     I'm kind of curious how you've decided that 30,000 square foot per floor 
> exceeds the allowable floor space per riser.  Aren't the values in 8.2.1 
> supposed to be applied to any one floor area? 
> Ken Wagoner, SET
> Parsley Consulting
> 350 West 9th Avenue, Suite 206
> Escondido, California 92025
> Phone 760-745-6181
> Visit our website
> 
> On 09/01/2016 10:45 AM, Jeff Bridges wrote:
> I would respectfully disagree with the below analogy.
> Example: (4) Story building consisting of 30K SF per floor
> Single lead-in supply- combo standpipe with floor controls.
> How can it be considered a single system when it exceeds the allowable floor 
> space per riser?
> Just sayin’
>  
> Jeff Bridges
> JBFP Inc
>  
>  
>  
>  
> I have to disagree with this analysis that a floor control valve defines a 
> system. A floor control valve is not even defined individually in 2013 
> whereas a sprinkler system is (no mention of floor control valves) as are 
> control valves. As always, I would consider a system to be what it has always 
> been and the addition of the required floor control valve and associated 
> requirements on systems in multi-story buildings just nationally codifies a 
> common practice hereabouts of building a system that has isolatable floors. 
> This way an entire large building does not need to be drained to make a 
> repair or for a T.I., leaves fore protection in service on floors not 
> effected and also conserves water.  I'm open to an argument that changes my 
> mind but this one doesn't.
>  
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to