Uhhhhhh ... not sure those metrics matter or if I even understand the point 
you're making.

Once upon a time, floor controls were not required on multi-story buildings 
unless subject building was code-classified as high-rise.  Even then, the 
requirement to control and alarm each floor separately was (and still is) in 
the building code(s) and we just played along.   Since those days, we now have 
indoor plumbing AND clear prescriptions in NFPA 13 and 14 for when and how to 
sectionally control floors of a sprinkler system.  But it's still just one 
system with a single main riser unless there's more than one main riser.   
There is no limit to the number of standpipes you can install off of a single 
"system", but if you have floors greater than 52,000 sq. ft. in LH and/or OH 
occupancies, then you would need two sprinkler risers or "systems".   Where it 
gets confusing to me is whether you can select two standpipes in a single 
system (as defined by NFPA 14) and make them combination to fulfill the 
requirement, or whether you would need a completely separate system with its 
own connection to a water supply and dedicated riser.

Perhaps someone can enlighten me, but it appears that the 2013 requirement for 
floor control assemblies in buildings 2-stories in height has been taken out of 
the standard.  So I guess the status quo in 13 depends on which edition you're 
using, but in a non-high-rise building, NFPA 14 affords you the option of 
creating combination standpipes but requires that for every sprinkler 
connection there must be a control and check valve.  So except for the 
requirement to sectionally alarm each floor as in a high-rise, you have a 
defacto floor control assembly in practice.   However, none of this creates a 
separate "system" horizontally, IMHO.

The foregoing is my opinion only and is not intended to represent the NFPA 14 
Technical Committee, nor serve as an interpretation of the standard.

Steve Leyton
Protection Design & Consulting
San Diego, CA





From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jeff Bridges
Sent: Thursday, September 01, 2016 11:31 AM
To: [email protected]
Subject: RE: 5 year fire sprinkler Obstruction Assessment - What items in a 
system define it as a separate wet pipe system?

I didn't
I was showing if it all is one system as Ron was eluding to, floor controls not 
considered as separation, the cumulative total of floor space being covered 
under a single riser would be 120K
BUT if floor controls ARE considered as a riser, each RISER is covering 30K.
I never said that 30K is a max per riser but if, under my example, floor 
controls are merely considered making the system easier to drain and not a 
separate system, then it exceeds 52K as allowed.
Right?

Jeff Bridges
JB Fire Protection Inc
(888) 523-4737 Fax (714) 578-0901
Fire Sprinklers Save Lives & Property
www.jbfireprotection.com<http://www.jbfireprotection.com/>

This email transmission (and any of its attachments) is intended only for the 
person or entity to whom it is addressed, and may contain confidential, 
proprietary and/or privileged information. No waiver of any applicable 
privileges or protections is intended hereby. If you are not the person to whom 
this transmission is addressed, you are hereby notified that the disclosure, 
copying, distribution, reliance upon or use of any of the information contained 
in this transmission is strictly prohibited. If you have received this 
transmission in error, delete any copies which may exist on your system and 
notify the sender immediately. This email transmission cannot be guaranteed 
secure or error-free. Any views expressed in this message are those of the 
individual sender, except where the sender specifies them to be the views of 
the company and is authorized to do so.


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Parsley Consulting
Sent: Thursday, September 01, 2016 11:07 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: 5 year fire sprinkler Obstruction Assessment - What items in a 
system define it as a separate wet pipe system?

Jeff,
    I'm kind of curious how you've decided that 30,000 square foot per floor 
exceeds the allowable floor space per riser.  Aren't the values in 8.2.1 
supposed to be applied to any one floor area?
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit our website<http://www.parsleyconsulting.com/>
On 09/01/2016 10:45 AM, Jeff Bridges wrote:
I would respectfully disagree with the below analogy.
Example: (4) Story building consisting of 30K SF per floor
Single lead-in supply- combo standpipe with floor controls.
How can it be considered a single system when it exceeds the allowable floor 
space per riser?
Just sayin'

Jeff Bridges
JBFP Inc




I have to disagree with this analysis that a floor control valve defines a 
system. A floor control valve is not even defined individually in 2013 whereas 
a sprinkler system is (no mention of floor control valves) as are control 
valves. As always, I would consider a system to be what it has always been and 
the addition of the required floor control valve and associated requirements on 
systems in multi-story buildings just nationally codifies a common practice 
hereabouts of building a system that has isolatable floors. This way an entire 
large building does not need to be drained to make a repair or for a T.I., 
leaves fore protection in service on floors not effected and also conserves 
water.  I'm open to an argument that changes my mind but this one doesn't.




_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to