I was just wanting to help out. Since I have designed to 13R and 13D and
once submitted they rejected saying that although it met 13R or 13D but not
IBC.

 

Sorry for trying to help. I'll just read what the experts post and keep my
opinion to myself. 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Steve Leyton
Sent: November-07-16 11:27 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: 13D Porches

 

What am I missing here?    The question is whether 13D (that's "Thirteen
Dee") requires sprinklers in porches and we've got a thread that's turning
toward the IBC.   If the dwelling(s) in question are being built per the IBC
then I don't think 13D would be the correct standard in the first place.

 

SL

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Monday, November 07, 2016 8:18 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: 13D Porches

 

CHECK IBC. I THINK IT WILL REQUIRE THEM.

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Roland Huggins
Sent: November-07-16 11:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: 13D Porches

 

I would say OPEN is to the temperature, not the bugs.  Also look at it from
the potential to flash-over.  The screen will not hold in the heat.  Now
have that discussion with the AHJ.

 

The TC member caveat - Not to be considered a formal interpretation of NFPA

 

Roland

 

 

Roland Huggins, PE - VP Engineering

American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives

Dallas, TX

http://www.firesprinkler.org <http://www.firesprinkler.org/> 

 

 

 

On Nov 6, 2016, at 4:58 PM, Todd Williams <fpdcdes...@gmail.com> wrote:

 

 
<https://tr.cloudmagic.com/h/v6/emailtag/tag/1478480303/2d4c4b9cd9f303a04c4d
9c24d32f6571/ecdd64c309bb34b23eb65c654267bfff/4320b82257e7b25d61f3e788b5efb0
03/9efab2399c7c560b34de477b9aa0a465/ufo.gif> 

NFPA 13D allows for exclusion of sprinklers in open attached porches. Does
screening count as an enclosure?

Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-608-4559 (cell)

 

via Newton Mail
<https://cloudmagic.com/k/d/mailapp?ct=ti&cv=9.2.5&pv=10.1.1&source=email_fo
oter_2> 

 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to