No, no that's not the spirit of my comment.  I just chose yours for response 
because it was the most recent but the implication was that this is being over 
thought.   The question perhaps should be, "Is a screen porch a room?"    Is 
"Porch" a defined term in the IRC or the sprinkler standard?     Apologies if 
my comment seemed gruff - it was not meant to be.   Post away ...

SL

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Monday, November 07, 2016 8:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: 13D Porches

I was just wanting to help out. Since I have designed to 13R and 13D and once 
submitted they rejected saying that although it met 13R or 13D but not IBC.

Sorry for trying to help. I'll just read what the experts post and keep my 
opinion to myself.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: November-07-16 11:27 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: 13D Porches

What am I missing here?    The question is whether 13D (that's "Thirteen Dee") 
requires sprinklers in porches and we've got a thread that's turning toward the 
IBC.   If the dwelling(s) in question are being built per the IBC then I don't 
think 13D would be the correct standard in the first place.

SL

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Monday, November 07, 2016 8:18 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: 13D Porches

CHECK IBC. I THINK IT WILL REQUIRE THEM.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: November-07-16 11:10 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: 13D Porches

I would say OPEN is to the temperature, not the bugs.  Also look at it from the 
potential to flash-over.  The screen will not hold in the heat.  Now have that 
discussion with the AHJ.

The TC member caveat - Not to be considered a formal interpretation of NFPA

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org<http://www.firesprinkler.org/>



On Nov 6, 2016, at 4:58 PM, Todd Williams 
<fpdcdes...@gmail.com<mailto:fpdcdes...@gmail.com>> wrote:

[https://tr.cloudmagic.com/h/v6/emailtag/tag/1478480303/2d4c4b9cd9f303a04c4d9c24d32f6571/ecdd64c309bb34b23eb65c654267bfff/4320b82257e7b25d61f3e788b5efb003/9efab2399c7c560b34de477b9aa0a465/ufo.gif]
NFPA 13D allows for exclusion of sprinklers in open attached porches. Does 
screening count as an enclosure?
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-608-4559 (cell)

via Newton 
Mail<https://cloudmagic.com/k/d/mailapp?ct=ti&cv=9.2.5&pv=10.1.1&source=email_footer_2>

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>